    hello, I have entered the modbus RTU data, then the data has appeared on scada. but the data sent by modbus is 27.3 then the data displayed in scada is 273.00. then how do I change it?

    #13544
    Mikhail
    Moderator

    Hello,
    Set the channel formula
    Cnl/10

    #13546
    chika
    Participant

    Sorry, there is a miss understanding about my last question. Here is what i actually mean :
    I mean, if i have data 273 from modbusRTU but i want to display it as 27.3 on scada tables view. I have tried but, the data show is 273.00. Can you help me to solve this?
    Thanks you mr. Mikhail

    #13548
    Mikhail
    Moderator

    Could you provide a screenshot of the Channels table?

    #13555
    chika
    Participant

    I HAVE SUCCESSFUL, THANK YOU FOR YOUR HELP