Changing setpoint values for a Modbus Device

Forum Home Forums Communicating with Devices Changing setpoint values for a Modbus Device

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #4640
    btrindade
    Participant

    I’m new working with rapid scada. Regarding the installation and configuration, watching your videos I’ve understood it. Also changing digital values is simple, but I need to read and write setpoint values (Holding Register 32 Bit Float) and I’m only able to read but not to write. How can this be done? I’ve searched through the forum but haven’t found how it’s done. Can you help me?

    #4643
    Mikhail
    Moderator

    Hi,

    1. You need to create commands in the Modbus template.
    Test that the commands work well in Communicator.

    2. Create output channels using Administrator and configure user interface.

    In case of follow up questions, please provide screenshots of your settings and communication logs.