cannot get opc da value

Forum Home Forums Communicating with Devices OPC cannot get opc da value

Viewing 11 posts - 1 through 11 (of 11 total)
  • Author
    Posts
  • #13458
    william
    Participant

    I am trying to read opc da data using scada v6. I can connect to the OPC DA server and add data nodes, but reading the node value failed and the log indicates that access is denied. I used Wireshark to capture traffic and found that there was no username passed in the authentication information. As shown in the following figure.
    scada_pcap
    On the same computer, I can read OPC DA data normally using the “OPC client” software. The authentication information of this software includes the username. As shown in the following figure.
    opc_client_pcap
    I don’t know why, please help me. thanks.

    #13460
    Mikhail
    Moderator

    Possible reason is that Communicator works as a service while another app is a desktop application.
    You can try setting username, password and domain in the connection parameters of the OPC device.
    What is OPC DA specification version?
    What is the OPC server you try to connect?

    • This reply was modified 1 year ago by Mikhail.
    #13462
    william
    Participant

    Thanks for your reply.
    The OPC DA specification version is 2.0
    The OPC server is a DCS device.
    I will go to the factory and give it a try. I will report the results after trying.

    #13463
    william
    Participant

    Setting username, password and domain does not work.
    The Communicator still cannot read value. The error in the log is E_NETWORK_ERROR.
    But connecting in the device properties page can be successful. Perhaps the device properties page like a desktop application and the Communicator is a service.
    Are there any other configurations that I can try?

    #13464
    Mikhail
    Moderator

    Could you copy communication line log here?

    #13465
    william
    Participant

    line000.log :
    ——————————————————————————–
    ——————————————————————————–
    2023-09-27 12:29:18 Start communication line [0] int0

    2023-09-27 12:29:18 Connect to OPCServer.WinCC/{75d00bbb-dda5-11d1-b944-9e614d000000}
    2023-09-27 12:29:19 Error connecting OPC server:
    E_NETWORK_ERROR
    Could not connect to server.

    2023-09-27 12:29:19 Delay before connecting 4.4 sec
    2023-09-27 12:29:23 Connect to OPCServer.WinCC/{75d00bbb-dda5-11d1-b944-9e614d000000}
    2023-09-27 12:29:23 Error connecting OPC server:
    E_NETWORK_ERROR
    Could not connect to server.

    *********************************************
    device000.txt :
    [0] dcsda1
    ———-
    Driver : DrvOpcClassic 6.0.0.0
    Status : Error
    Session time : Undefined
    Command time : Undefined

    Sessions (total / errors) : 0 / 0
    Commands (total / errors) : 0 / 0
    Requests (total / errors) : 0 / 0

    Current Data
    +—+——+——+——-+———+
    | # | Code | Name | Value | Channel |
    +—+——+——+——-+———+
    | ************* opcda ************* |
    +—+——+——+——-+———+
    | 1 | a1 | a1 | — | |
    +—+——+——+——-+———+

    ***********************************************
    ScadaComm.log
    ——————————————————————————–
    2023-09-27 12:29:15 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Communicator 6.1.1.1 started
    2023-09-27 12:29:15 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Storage FileStorage 6.1.0.0 loaded from file C:\Program Files\SCADA\ScadaComm\FileStorage.dll
    2023-09-27 12:29:15 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Start logic processing
    2023-09-27 12:29:15 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Driver DrvDsScadaServer 6.0.1.1 loaded from file C:\Program Files\SCADA\ScadaComm\Drv\DrvDsScadaServer.Logic.dll
    2023-09-27 12:29:15 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Driver DrvOpcClassic 6.0.0.0 loaded from file C:\Program Files\SCADA\ScadaComm\Drv\DrvOpcClassic.Logic.dll
    2023-09-27 12:29:15 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Data source ScadaServer initialized successfully
    2023-09-27 12:29:15 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Data source ScadaServer: Receive the configuration database
    2023-09-27 12:29:18 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Data source ScadaServer: The configuration database has been received successfully
    2023-09-27 12:29:18 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Start communication lines
    2023-09-27 12:29:18 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Start reading commands from files
    2023-09-27 12:29:20 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Data source ScadaServer: Connection state is Logged In
    2023-09-27 12:35:09 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Stop communication lines
    2023-09-27 12:35:14 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] All communication lines are stopped
    2023-09-27 12:35:14 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Logic processing is stopped
    2023-09-27 12:35:14 [DESKTOP-KJ7BBFJ][DESKTOP-KJ7BBFJ$][ACT] Communicator is stopped
    ——————————————————————————–

    #13466
    Mikhail
    Moderator

    Try Solution 1 and Solution 2 described at the bottom of this article.

    #13467
    Mikhail
    Moderator

    This page also may help.

    #13470
    william
    Participant

    It’s working! Thank you very much!

    #13472
    Mikhail
    Moderator

    How did you solve this issue?

    #13485
    william
    Participant

    Follow the solution 1 and 2 described in the article you provided.