ramboParticipant
Sir,
Communicator status is ok… but there is no change in data, but this is a normal condition for this case, and it should not be changed to 5 … is it possible.?
ramboParticipantOk What about MQTT and R gate … where to enter the Licence key
ramboParticipantramboParticipantHello Mikhail,
Its long time , but I am back on rapid scada:))
It seems fthe following formula doent work properly
Cnl/1000; CorrectStat()
any clue
ramboParticipantYou are right ….
Its working now… thanks a lot.
ramboParticipantFor the old set up only …. in old also set up is defined in interface section of scada admin, my created table “test 1” is not listed here, but in web application I can see it.
ramboParticipantOk,
1 observation is there,
In my set up the new table “test 1” is not listed in interface section of scada admin, as you are asking to define views in the link above, I have simply configured the scada web configurator, and after restarting of server I am able to see the table in same set of SERVER ROOM in scada web application,
can that be one of possible cause of mis behaviour.
Regards,ramboParticipantis there some stability issue with web app??
I am planning to take this on project level… may be plan for pro chart and auto modules stability and robust system is a prime requirement.
Should I get worried ??
ramboParticipantAlso Virtual Memory size is 4096 MB, in task manager I have seen RAM usage go uptp 2.9GB out of 3.9GB phisical RAM, also disk usage was also running high at the tune of 80%-90%, ( I have not observed it during other routine work) …
Any clue for crash???
Regards,
ramboParticipantIn channel column no input channel are displayed….
I have tried services creating channels in scada admin but it says, error created channels are missing…
How to resolve this…..
Regards,
ramboParticipantHello Mikhail,
thanx for reply, Its still not working,
I think I have still not understood the basic working and interlinking of all the applications,
For now i am trying to simulate server room:-
t4 (10000 decimal) (Burnout4 is set to 1) and t5( decimal 11000) (Burnout5 is set to 1) values are received by scadacomm, and communication line 1 is bound to server, but in scada web i am not getting any update.
I have tried generator of scada server, its work fine in web..
but in normal comm process i am not getting scada web upgarede.
Please suggest what to look for.
Regards
ramboParticipantDear Mikhail ,
I have tried it but it did not work.
In formulas A pasted in source code section
public double GetByte(double val, int n)
{
UInt64 uintVal = (UInt64)val;
return (uintVal >> (n*8)) & 0xFF;
}
then in i/p channel formula
(((256*GetByte(Cnl,3))+GetByte(Cnl,2))+(GetByte(Cnl,1)/256)+(GetByte(Cnl,0)/(256*256)))/10
Communication log is as follows I have
2016-06-24 01:24:48 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 09 AC 74 47
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 07 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!But in Communicator device data , I did not find any change.
Device 38 “mod simulator”
————————-
DLL : KpModbus
State : undefined
Comm. session : 24/06/2016 01:34:04
Command : time is undefinedComm. sessions (total / errors) : 5 / 0
Commands (total / errors) : 0 / 0
Requests (total / errors) : 10 / 0Current device tags data
+——–+———+——-+———+
| Signal | Name | Value | Channel |
+——–+———+——-+———+
| ******** Voltage ***************** |
+——–+———+——-+———+
| 1 | Va | 0.000 | |
+——–+———+——-+———+
| ******** Current ***************** |
+——–+———+——-+———+
| 2 | Ia | 0.000 | |
+——–+———+——-+———+No archive data
No events
I have even tried putting direct formula i.e.
((256*9)+172+(116/256)+(71/(256*256)))/10
at formula of i/p channel but still no result,
I think I have not understood how to use formula.
Pls help how to go now,
Thanx & Regards
ramboParticipantThanx..
ramboParticipantDear Mikhail,
Thanx for reply….
I have manipulate with period and delays now I am getting stable connection.
2016-06-21 17:34:04 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1A 00 1A
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 07 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1A 00 1A
OK!2016-06-21 17:34:06 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1B 00 1B
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 07 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1B 00 1B
OK!2016-06-21 17:34:08 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1B 00 1B
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 07 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1B 00 1B
OK!2016-06-21 17:34:10 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1C 00 1C
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 07 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1C 00 1C
OK!2016-06-21 17:34:12 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1D 00 1D
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 07 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1D 00 1D
OK!2016-06-21 17:34:14 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1E 00 1E
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 07 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1E 00 1E
OK!2016-06-21 17:34:16 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1F 00 1F
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 07 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 1F 00 1F
OK!I am increasing the word in simulation to change the 4X registers …. as u can see in the log…
Now how to fetch the required information from this data…..
voltage reg received is say (09 AC 74 47) , manufactrur says consider it as (P, Q, R , S), then apply formula (((256*P)+Q)+(R/256)+(S/(256*256)))/10 that is final voltage value 247.64 how to apply this formula and get value..
Thanx
ramboParticipantroot cause is identified…. my mistake I am trying to communicate over TCP with simulator, but in scada communicator device properties i selected modbus RTU.
Now I get communication established and values are comming … but after some time it give error.
——————————————————————————–
2016-06-21 10:43:55 Initialize communication line 7 “read test”
2016-06-21 10:43:55 Load device template from file meter1_one byte.xml
2016-06-21 10:43:56 Start communication line 7 “read test”2016-06-21 10:43:56 Establish a TCP connection with 127.0.0.1:502
2016-06-21 10:43:56 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!2016-06-21 10:43:56 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!2016-06-21 10:43:57 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!2016-06-21 10:43:58 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!2016-06-21 10:43:58 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!2016-06-21 10:43:59 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 00 00 00
OK!2016-06-21 10:44:00 Stop communication line 7 “read test”
——————————————————————————–
——————————————————————————–
2016-06-21 10:44:24 Initialize communication line 7 “read test”
2016-06-21 10:44:24 Load device template from file meter1_one byte.xml
2016-06-21 10:44:24 Start communication line 7 “read test”2016-06-21 10:44:24 Establish a TCP connection with 127.0.0.1:502
2016-06-21 10:44:24 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 03 00 03
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 03 00 03
OK!2016-06-21 10:44:25 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 03 00 03
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 03 00 03
OK!2016-06-21 10:44:25 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 04 00 04
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 04 00 04
OK!2016-06-21 10:44:26 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 04 00 04
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 04 00 04
OK!2016-06-21 10:44:27 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 04 00 04
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 04 00 04
OK!2016-06-21 10:44:27 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 04 00 04
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 05 00 05
OK!2016-06-21 10:44:28 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 05 00 05
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 05 00 05
OK!2016-06-21 10:44:29 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 05 00 05
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 05 00 05
OK!2016-06-21 10:44:30 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 05 00 05
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 05 00 05
OK!2016-06-21 10:44:30 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 06 00 06
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 06 00 06
OK!2016-06-21 10:44:31 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 06 00 06
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 06 00 06
OK!2016-06-21 10:44:32 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 06 00 06
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 06 00 06
OK!2016-06-21 10:44:32 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 06 00 06
OK!
Request element group “Current”
Send (12): 00 00 00 00 00 06 04 03 00 06 00 02
Receive (7/7): 00 00 00 00 00 07 04
Receive (6/6): 03 04 00 07 00 07
OK!2016-06-21 10:44:33 Stop communication line 7 “read test”
——————————————————————————–
——————————————————————————–
2016-06-21 10:44:35 Initialize communication line 7 “read test”
2016-06-21 10:44:35 Load device template from file meter1_one byte.xml
2016-06-21 10:44:35 Start communication line 7 “read test”2016-06-21 10:44:35 Establish a TCP connection with 127.0.0.1:502
2016-06-21 10:44:35 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!2016-06-21 10:44:42 Disconnect from 127.0.0.1
2016-06-21 10:44:42 Establish a TCP connection with 127.0.0.1:502
2016-06-21 10:44:42 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!2016-06-21 10:44:48 Disconnect from 127.0.0.1
2016-06-21 10:44:49 Establish a TCP connection with 127.0.0.1:502
2016-06-21 10:44:49 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!2016-06-21 10:44:55 Disconnect from 127.0.0.1
2016-06-21 10:44:55 Establish a TCP connection with 127.0.0.1:502
2016-06-21 10:44:55 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!2016-06-21 10:45:02 Disconnect from 127.0.0.1
2016-06-21 10:45:02 Stop communication line 7 “read test”
——————————————————————————–
——————————————————————————–
2016-06-21 10:46:24 Initialize communication line 7 “read test”
2016-06-21 10:46:24 Load device template from file meter1_one byte.xml
2016-06-21 10:46:25 Start communication line 7 “read test”2016-06-21 10:46:25 Establish a TCP connection with 127.0.0.1:502
2016-06-21 10:46:25 Communication session with the Device 38 “mod simulator”, type: KpModbus, address: 4, call number: 127.0.0.1
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!
Request element group “Voltage”
Send (12): 00 00 00 00 00 06 04 03 00 05 00 02
Receive (0/7):
Communication error!2016-06-21 10:46:30 Disconnect from 127.0.0.1
2016-06-21 10:46:30 Stop communication line 7 “read test”
-