C_D
  • in reply to: Excel Exporting #1069
    C_D
    Mikhail,
    The new minute data report is exactly what I needed. Thank you so much.
    in reply to: Modbus Byte Order #1068
    C_D
    Mikhail,
    I installed the new version of RapidSCADA this morning and can confirm that this bug is now fixed.
    Much appreciated.
    in reply to: I cant see Scada Comunicator window #1020
    C_D
    I observed this also, is there a reason it starts up minimised to the tray?
    in reply to: Excel Exporting #1019
    C_D
    This sounds perfect. Can you send it to me so I can trial the report now, or will I need to wait till the installation package is updated and do a reinstall?
    in reply to: Modbus Byte Order #1001
    C_D
    If I remove device 11 (the working one), Device 21 now starts decoding correctly and the others remain incorrect.
    It looks very much like the byte order is only being applied to the first device in the list, not all of them. Even though they are all using the same template.
    EDIT:
    If I create a separate communication line for each Device, I can make each one work correctly on its own. But obviously this doesn’t work when you try and use more than one since they are sharing the same COM port.
    • This reply was modified 10 years, 7 months ago by C_D.
    in reply to: Modbus Byte Order #998
    C_D
    Is this what you were after?
    You can see data in the messages is correct. The conversion for Device 11 was correct, but for all the others the value has been decoded with the wrong byte order. For the incorrect devices, decoding the message as sent (without reordering the bytes) produces the exact numbers that are displayed.
    2016-04-21 09:36:54 Communication session with the Device 21 "Power Monitor TR2 Left", type: KpModbus, address: 7
    Request element group "Voltage"
    Send (8): 07 04 00 00 00 02 71 AD
    Receive (5/5): 07 04 04 0F F7
    Receive (4/4): 43 69 DE 7C
    OK!
    2016-04-21 09:36:54 Communication session with the Device 31 "Power Monitor TR3 Left", type: KpModbus, address: 10
    Send (8): 0A 04 00 00 00 02 70 B0
    Receive (5/5): 0A 04 04 CA C4
    Receive (4/4): 43 68 0F BF
    OK!
    2016-04-21 09:36:55 Communication session with the Device 32 "Power Monitor TR3 Right", type: KpModbus, address: 11
    Send (8): 0B 04 00 00 00 02 71 61
    Receive (5/5): 0B 04 04 5D E8
    Receive (4/4): 43 69 33 02
    OK!
    2016-04-21 09:36:55 Communication session with the Device 11 "Power Monitor TR1", type: KpModbus, address: 9
    Send (8): 09 04 00 00 00 02 70 83
    Receive (5/5): 09 04 04 A4 75
    Receive (4/4): 43 69 B1 B0
    OK!
    DLL           : KpModbus
    State         : undefined
    Comm. session : 21/04/2016 09:36:54
    Command       : time is undefined
    Comm. sessions (total / errors) : 14 / 0
    Commands       (total / errors) : 0 / 0
    Requests       (total / errors) : 14 / 0
    Current device tags data
    | Signal | Name    | Value | Channel |
    | ******** Voltage ***************** |
    |      1 | V L1-N  | 0.000 |     121 |
    DLL           : KpModbus
    State         : undefined
    | ******** Voltage ************************** |
    |      1 | V L1-N  | -6,431,156.000 |     181 |
    DLL           : KpModbus
    State         : undefined
    Comm. session : 21/04/2016 09:36:55
    | ******** Voltage ***************************************** |
    |      1 | V L1-N  | 2,092,042,011,119,980,000.000 |     241 |
    DLL           : KpModbus
    State         : undefined
    Comm. sessions (total / errors) : 15 / 0
    Requests       (total / errors) : 15 / 0
    | ******** Voltage ******************* |
    |      1 | V L1-N  | 233.642 |      61 |
    So manually decoding them again:
    TR2 Left:
    Receive: 0F F7 43 69
    Reorder: 43 69 0F F7
    Decode: 233.06236
    Decode without reorder: 2.4382046E-29 (rounds to 0.000)
    Displayed: 0.000
    TR3 Left:
    Receive: CA C4 43 68
    Reorder: 43 68 CA C4
    Decode: 232.79205
    Decode without reorder: -6431156.0
    Displayed: -6,431,156.000
    TR3 Right:
    Receive: 5D E8 43 69
    Reorder: 43 69 5D E8
    Decode: 233.36682
    Decode without reorder: 2.09204201E18
    Displayed: 2,092,042,011,119,980,000.000
    TR1:
    Receive: A4 75 43 69
    Reorder: 43 69 A4 75
    Decode: 233.64241
    Displayed: 233.642
    in reply to: Modbus Byte Order #991
    C_D
    Just as a sanity check i will pull some of those numbers out and convert them. This is the first register read from each device (thats a good one to test because it should have a value around 230V).
    Unfortunately it looks like my log of the displayed data doesn’t match exactly to the Communication Log, im guessing it updated a few times in between me pasting one and then pasting the next. But you can see the in the Communication Log all the data is reasonable, while in the displayed data all apart from the first device is wrong.
    Device 11:
    Raw: 4D 0D 43 66
    Reordered: 43 66 4D 0D
    Converted: 230.30098
    Displayed: 231.481
    Device 21:
    Raw: E7 AC 43 65
    Reordered: 43 65 E7 AC
    Converted: 229.90497
    Displayed: 0.042
    Device 31:
    Raw: 8C 76 43 65
    Reordered: 43 65 8C 76
    Converted: 229.54868
    Displayed: 0.001
    Device 32:
    Raw: 9C 1B 43 65
    Reordered: 43 65 9C 1B
    Converted: 229.60979
    Displayed: -127,659,305,253,422,000,000,000.000
    in reply to: Modbus Byte Order #989
    C_D
    Mikhail,
    I have been using that calculator already to check my data. Here is a full communication log for all my sensors. One is not configured at the moment so it skips over it.
    Device 11 – TR1: this is correct.
    Device 21 – TR2-L: this is wrong.
    Device 22 – TR2-R: this is not configured.
    Device 31 – TR3-L: this is wrong.
    Device 32 – TR3-R: this is wrong.
    2016-04-20 07:24:10 Communication session with the Device 11 "Power Monitor TR1", type: KpModbus, address: 9
    Send (8): 09 04 00 00 00 0C F1 47
    Receive (5/5): 09 04 18 4D 0D
    Receive (24/24): 43 66 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 27 89
    OK!
    Request element group "Current"
    Send (8): 09 04 00 0C 00 08 30 87
    Receive (5/5): 09 04 10 00 00
    Receive (16/16): 00 00 00 00 00 00 00 00 00 00 00 00 00 00 B7 4D
    OK!
    Request element group "Real Power (W)"
    Send (8): 09 04 00 14 00 06 31 44
    Receive (5/5): 09 04 0C 00 00
    Receive (12/12): 00 00 00 00 00 00 00 00 00 00 9D B1
    OK!
    Request element group "Apparent Power (VA)"
    Send (8): 09 04 00 1A 00 06 50 87
    OK!
    Request element group "VAR"
    Send (8): 09 04 00 20 00 06 70 8A
    Receive (12/12): 80 00 00 00 80 00 00 00 80 00 E4 59
    OK!
    Request element group "Phase Sequence"
    Send (8): 09 04 00 26 00 02 91 48
    Receive (5/5): 09 04 04 00 00
    Receive (4/4): 3F 80 62 14
    OK!
    Request element group "Power Factor"
    Send (8): 09 04 00 28 00 06 F1 48
    Receive (12/12): 3F 80 00 00 3F 80 00 00 3F 80 D8 39
    OK!
    Request element group "Sums"
    Send (8): 09 04 00 2E 00 0C 91 4E
    Receive (5/5): 09 04 18 5C 07
    Receive (24/24): 43 66 5C 07 43 66 00 00 00 00 00 00 00 00 00 00 80 00 00 00 3F 80 01 0C
    OK!
    Request element group "Frequency"
    Send (8): 09 04 00 3A 00 02 50 8E
    Receive (5/5): 09 04 04 29 01
    Receive (4/4): 42 48 1B 4E
    OK!
    Request element group "Asymmetry"
    Send (8): 09 04 00 3C 00 04 30 8D
    Receive (5/5): 09 04 08 00 00
    Receive (8/8): 42 C8 00 00 00 00 E0 9F
    OK!
    Request element group "Demand"
    Send (8): 09 04 00 40 00 16 71 58
    Receive (5/5): 09 84 03 82 C3
    Device error: [03] ILLEGAL DATA VALUE!
    2016-04-20 07:24:13 Communication session with the Device 21 "Power Monitor TR2 Left", type: KpModbus, address: 7
    Send (8): 07 04 00 00 00 0C F0 69
    Receive (5/5): 07 04 18 E7 AC
    Receive (24/24): 43 65 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 75 C5
    OK!
    Send (8): 07 04 00 0C 00 08 31 A9
    Receive (5/5): 07 04 10 28 C8
    Receive (16/16): 40 08 00 00 00 00 00 00 00 00 9E FB 40 07 7B 3F
    OK!
    Send (8): 07 04 00 14 00 06 30 6A
    Receive (5/5): 07 04 0C 26 7A
    Receive (12/12): 43 EC 00 00 00 00 00 00 00 00 7F 04
    OK!
    Send (8): 07 04 00 1A 00 06 51 A9
    Receive (5/5): 07 04 0C F1 33
    Receive (12/12): 43 F4 00 00 00 00 00 00 00 00 99 2C
    OK!
    Send (8): 07 04 00 20 00 06 71 A4
    Receive (5/5): 07 04 0C 40 4A
    Receive (12/12): 42 FA 00 00 80 00 00 00 80 00 C1 29
    OK!
    Send (8): 07 04 00 26 00 02 90 66
    Receive (5/5): 07 04 04 00 00
    Receive (4/4): 3F 80 8D D4
    OK!
    Send (8): 07 04 00 28 00 06 F0 66
    Receive (5/5): 07 04 0C A6 0C
    Receive (12/12): 3F 77 00 00 3F 80 00 00 3F 80 C0 90
    OK!
    Send (8): 07 04 00 2E 00 0C 90 60
    Receive (5/5): 07 04 18 CA 72
    Receive (24/24): 43 65 CA 72 43 65 F7 85 43 F0 DF 12 43 F8 E5 D8 42 F8 DE 7D 3F 77 97 A7
    OK!
    Send (8): 07 04 00 3A 00 02 51 A0
    Receive (5/5): 07 04 04 0F 61
    Receive (4/4): 42 48 FF D8
    OK!
    Send (8): 07 04 00 3C 00 04 31 A3
    Receive (5/5): 07 04 08 00 00
    Receive (8/8): 42 C8 00 00 00 00 D4 77
    OK!
    Send (8): 07 04 00 40 00 16 70 76
    Receive (5/5): 07 84 03 E3 00
    2016-04-20 07:24:17 Communication session with the Device 22 "Power Monitor TR2 Right", type: KpModbus, address: 8
    Normal device communication is impossible because device template has not been loaded
    2016-04-20 07:24:17 Communication session with the Device 31 "Power Monitor TR3 Left", type: KpModbus, address: 10
    Send (8): 0A 04 00 00 00 0C F1 74
    Receive (5/5): 0A 04 18 8C 76
    Receive (24/24): 43 65 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 4D B4
    OK!
    Send (8): 0A 04 00 0C 00 08 30 B4
    Receive (5/5): 0A 04 10 00 00
    Receive (16/16): 00 00 00 00 00 00 00 00 00 00 00 00 00 00 F3 09
    OK!
    Send (8): 0A 04 00 14 00 06 31 77
    Receive (5/5): 0A 04 0C 00 00
    Receive (12/12): 00 00 00 00 00 00 00 00 00 00 DE B0
    OK!
    Send (8): 0A 04 00 1A 00 06 50 B4
    OK!
    Send (8): 0A 04 00 20 00 06 70 B9
    Receive (12/12): 00 00 00 00 80 00 00 00 80 00 A0 B0
    OK!
    Send (8): 0A 04 00 26 00 02 91 7B
    Receive (5/5): 0A 04 04 00 00
    Receive (4/4): BF 80 30 D4
    OK!
    Send (8): 0A 04 00 28 00 06 F1 7B
    Receive (12/12): 3F 80 00 00 3F 80 00 00 3F 80 9B 38
    OK!
    Send (8): 0A 04 00 2E 00 0C 91 7D
    Receive (5/5): 0A 04 18 74 F8
    Receive (24/24): 43 65 74 F8 43 65 00 00 00 00 00 00 00 00 00 00 00 00 00 00 3F 80 EA 97
    OK!
    Send (8): 0A 04 00 3A 00 02 50 BD
    Receive (5/5): 0A 04 04 F0 A8
    Receive (4/4): 42 47 83 36
    OK!
    Send (8): 0A 04 00 3C 00 04 30 BE
    Receive (5/5): 0A 04 08 00 00
    Receive (8/8): 42 C8 00 00 00 00 EF DB
    OK!
    Send (8): 0A 04 00 40 00 16 71 6B
    Receive (5/5): 0A 84 03 72 C3
    2016-04-20 07:24:21 Communication session with the Device 32 "Power Monitor TR3 Right", type: KpModbus, address: 11
    Send (8): 0B 04 00 00 00 0C F0 A5
    Receive (5/5): 0B 04 18 9C 1B
    Receive (24/24): 43 65 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 48 40
    OK!
    Send (8): 0B 04 00 0C 00 08 31 65
    Receive (5/5): 0B 04 10 07 A0
    Receive (16/16): 41 00 00 00 00 00 00 00 00 00 19 AA 41 00 7A D2
    OK!
    Send (8): 0B 04 00 14 00 06 30 A6
    Receive (5/5): 0B 04 0C C2 73
    Receive (12/12): 44 E5 00 00 00 00 00 00 00 00 F5 26
    OK!
    Send (8): 0B 04 00 1A 00 06 51 65
    Receive (5/5): 0B 04 0C D9 78
    Receive (12/12): 44 E5 00 00 00 00 00 00 00 00 F4 26
    OK!
    Send (8): 0B 04 00 20 00 06 71 68
    Receive (5/5): 0B 04 0C C4 56
    Receive (12/12): 41 91 00 00 80 00 00 00 80 00 7E 30
    OK!
    Send (8): 0B 04 00 26 00 02 90 AA
    Receive (5/5): 0B 04 04 00 00
    Receive (4/4): BF 80 20 14
    OK!
    Send (8): 0B 04 00 28 00 06 F0 AA
    Receive (5/5): 0B 04 0C FD 38
    Receive (12/12): 3F 7F 00 00 3F 80 00 00 3F 80 64 7E
    OK!
    Send (8): 0B 04 00 2E 00 0C 90 AC
    Receive (5/5): 0B 04 18 F4 CA
    Receive (24/24): 43 65 F4 CA 43 65 1A AE 44 E6 1D 2B 44 E6 0E 38 41 87 FD 3B 3F 7F 82 CD
    OK!
    Send (8): 0B 04 00 3A 00 02 51 6C
    Receive (5/5): 0B 04 04 E3 DE
    Receive (4/4): 42 47 76 A8
    OK!
    Send (8): 0B 04 00 3C 00 04 31 6F
    Receive (5/5): 0B 04 08 00 00
    Receive (8/8): 42 C8 00 00 00 00 EB 27
    OK!
    Send (8): 0B 04 00 40 00 16 70 BA
    Receive (5/5): 0B 84 03 23 03
    And here are the matching printouts:
    DLL           : KpModbus
    State         : error
    Comm. session : 20/04/2016 07:26:29
    Comm. sessions (total / errors) : 4749 / 4749
    Requests       (total / errors) : 61737 / 14247
    | ******** Voltage ******************************* |
    |      1 | V L1-N              | 231.481 |      61 |
    |      2 | V L2-N              |   0.000 |      62 |
    |      3 | V L3-N              |   0.000 |      63 |
    |      4 | V L1-L2             |   0.000 |      64 |
    |      5 | V L2-L3             |   0.000 |      65 |
    |      6 | V L3-L1             |   0.000 |      66 |
    | ******** Current ******************************* |
    |      7 | A L1                |   0.000 |      67 |
    |      8 | A L2                |   0.000 |      68 |
    |      9 | A L3                |   0.000 |      69 |
    |     10 | A N                 |   0.000 |      70 |
    | ******** Real Power (W) ************************ |
    |     11 | W L1                |   0.000 |      71 |
    |     12 | W L2                |   0.000 |      72 |
    |     13 | W L3                |   0.000 |      73 |
    | ******** Apparent Power (VA) ******************* |
    |     14 | VA L1               |   0.000 |      74 |
    |     15 | VA L2               |   0.000 |      75 |
    |     16 | VA L3               |   0.000 |      76 |
    | ******** VAR *********************************** |
    |     17 | VAR L1              |   0.000 |      77 |
    |     18 | VAR L2              |   0.000 |      78 |
    |     19 | VAR L3              |   0.000 |      79 |
    | ******** Phase Sequence ************************ |
    |     20 | Phase Sequence      |   1.000 |      80 |
    | ******** Power Factor ************************** |
    |     21 | PF L1               |   1.000 |      81 |
    |     22 | PF L2               |   1.000 |      82 |
    |     23 | PF L3               |   1.000 |      83 |
    | ******** Sums ********************************** |
    |     24 | V L-N sum           | 231.048 |      84 |
    |     25 | V L-L sum           | 231.048 |      85 |
    |     26 | W sum               |   0.000 |      86 |
    |     27 | VA sum              |   0.000 |      87 |
    |     28 | VAR sum             |   0.000 |      88 |
    |     29 | PF sum              |   1.000 |      89 |
    | ******** Frequency ***************************** |
    |     30 | Hz                  |  49.990 |      90 |
    | ******** Asymmetry ***************************** |
    |     31 | Asymmetry L-N (%)   | 100.000 |      91 |
    |     32 | Asymmetry L-L (%)   |   0.000 |      92 |
    | ******** Demand ******************************** |
    |     33 | A L1 dmd            |     --- |      93 |
    |     34 | A L2 dmd            |     --- |      94 |
    |     35 | A L3 dmd            |     --- |      95 |
    |     36 | W L1 dmd            |     --- |      96 |
    |     37 | W L2 dmd            |     --- |      97 |
    |     38 | W L3 dmd            |     --- |      98 |
    |     39 | VA L1 dmd           |     --- |      99 |
    |     40 | VA L2 dmd           |     --- |     100 |
    |     41 | VA L3 dmd           |     --- |     101 |
    |     42 | W dmd               |     --- |     102 |
    |     43 | VA dmd              |     --- |     103 |
    | ******** Total Energy ************************** |
    |     44 | kWh tot.            |     --- |     104 |
    |     45 | KVARh tot.          |     --- |     105 |
    |     46 | KWh par.            |     --- |     106 |
    |     47 | KVARh par.          |     --- |     107 |
    | ******** Hours ********************************* |
    |     48 | Hours               |     --- |     108 |
    No archive data
    No events
    DLL           : KpModbus
    State         : error
    Comm. session : 20/04/2016 07:26:48
    Comm. sessions (total / errors) : 4750 / 4750
    Requests       (total / errors) : 61750 / 14250
    | ******** Voltage ******************************************************************************* |
    |      1 | V L1-N              |                                                   0.042 |     121 |
    |      2 | V L2-N              |                                                   0.000 |     122 |
    |      3 | V L3-N              |                                                   0.000 |     123 |
    |      4 | V L1-L2             |                                                   0.000 |     124 |
    |      5 | V L2-L3             |                                                   0.000 |     125 |
    |      6 | V L3-L1             |                                                   0.000 |     126 |
    | ******** Current ******************************************************************************* |
    |      7 | A L1                |                                                   0.000 |     127 |
    |      8 | A L2                |                                                   0.000 |     128 |
    |      9 | A L3                |                                                   0.000 |     129 |
    |     10 | A N                 |                                  -7,189,566,586,880.000 |     130 |
    | ******** Real Power (W) ************************************************************************ |
    |     11 | W L1                |                  26,635,203,039,483,000,000,000,000.000 |     131 |
    |     12 | W L2                |                                                   0.000 |     132 |
    |     13 | W L3                |                                                   0.000 |     133 |
    | ******** Apparent Power (VA) ******************************************************************* |
    |     14 | VA L1               |                                                   0.000 |     134 |
    |     15 | VA L2               |                                                   0.000 |     135 |
    |     16 | VA L3               |                                                   0.000 |     136 |
    | ******** VAR *********************************************************************************** |
    |     17 | VAR L1              |                                                   0.008 |     137 |
    |     18 | VAR L2              |                                                   0.000 |     138 |
    |     19 | VAR L3              |                                                   0.000 |     139 |
    | ******** Phase Sequence ************************************************************************ |
    |     20 | Phase Sequence      |                                                   0.000 |     140 |
    | ******** Power Factor ************************************************************************** |
    |     21 | PF L1               |                                                   0.000 |     141 |
    |     22 | PF L2               |                                                   0.000 |     142 |
    |     23 | PF L3               |                                                   0.000 |     143 |
    | ******** Sums ********************************************************************************** |
    |     24 | V L-N sum           |                                      19,765,344,256.000 |     144 |
    |     25 | V L-L sum           |                                      19,765,344,256.000 |     145 |
    |     26 | W sum               |        -355,590,926,015,742,000,000,000,000,000,000.000 |     146 |
    |     27 | VA sum              |                                    -842,918,920,192.000 |     147 |
    |     28 | VAR sum             |                                                   0.000 |     148 |
    |     29 | PF sum              |                                        -362,275,424.000 |     149 |
    | ******** Frequency ***************************************************************************** |
    |     30 | Hz                  | -20,292,235,163,454,000,000,000,000,000,000,000,000.000 |     150 |
    | ******** Asymmetry ***************************************************************************** |
    |     31 | Asymmetry L-N (%)   |                                                   0.000 |     151 |
    |     32 | Asymmetry L-L (%)   |                                                   0.000 |     152 |
    | ******** Demand ******************************************************************************** |
    |     33 | A L1 dmd            |                                                     --- |     153 |
    |     34 | A L2 dmd            |                                                     --- |     154 |
    |     35 | A L3 dmd            |                                                     --- |     155 |
    |     36 | W L1 dmd            |                                                     --- |     156 |
    |     37 | W L2 dmd            |                                                     --- |     157 |
    |     38 | W L3 dmd            |                                                     --- |     158 |
    |     39 | VA L1 dmd           |                                                     --- |     159 |
    |     40 | VA L2 dmd           |                                                     --- |     160 |
    |     41 | VA L3 dmd           |                                                     --- |     161 |
    |     42 | W dmd               |                                                     --- |     162 |
    |     43 | VA dmd              |                                                     --- |     163 |
    | ******** Total Energy ************************************************************************** |
    |     44 | kWh tot.            |                                                     --- |     164 |
    |     45 | KVARh tot.          |                                                     --- |     165 |
    |     46 | KWh par.            |                                                     --- |     166 |
    |     47 | KVARh par.          |                                                     --- |     167 |
    | ******** Hours ********************************************************************************* |
    |     48 | Hours               |                                                     --- |     168 |
    No archive data
    No events
    DLL           : KpModbus
    State         : error
    Comm. session : 20/04/2016 07:26:52
    Requests       (total / errors) : 0 / 0
    No device tags
    No archive data
    No events
    DLL           : KpModbus
    State         : error
    Comm. session : 20/04/2016 07:27:08
    Comm. sessions (total / errors) : 4751 / 4751
    Requests       (total / errors) : 61763 / 14253
    | ******** Voltage ***************************** |
    |      1 | V L1-N              | 0.001 |     181 |
    |      2 | V L2-N              | 0.000 |     182 |
    |      3 | V L3-N              | 0.000 |     183 |
    |      4 | V L1-L2             | 0.000 |     184 |
    |      5 | V L2-L3             | 0.000 |     185 |
    |      6 | V L3-L1             | 0.000 |     186 |
    | ******** Current ***************************** |
    |      7 | A L1                | 0.000 |     187 |
    |      8 | A L2                | 0.000 |     188 |
    |      9 | A L3                | 0.000 |     189 |
    |     10 | A N                 | 0.000 |     190 |
    | ******** Real Power (W) ********************** |
    |     11 | W L1                | 0.000 |     191 |
    |     12 | W L2                | 0.000 |     192 |
    |     13 | W L3                | 0.000 |     193 |
    | ******** Apparent Power (VA) ***************** |
    |     14 | VA L1               | 0.000 |     194 |
    |     15 | VA L2               | 0.000 |     195 |
    |     16 | VA L3               | 0.000 |     196 |
    | ******** VAR ********************************* |
    |     17 | VAR L1              | 0.000 |     197 |
    |     18 | VAR L2              | 0.000 |     198 |
    |     19 | VAR L3              | 0.000 |     199 |
    | ******** Phase Sequence ********************** |
    |     20 | Phase Sequence      | 0.000 |     200 |
    | ******** Power Factor ************************ |
    |     21 | PF L1               | 0.000 |     201 |
    |     22 | PF L2               | 0.000 |     202 |
    |     23 | PF L3               | 0.000 |     203 |
    | ******** Sums ******************************** |
    |     24 | V L-N sum           | 0.000 |     204 |
    |     25 | V L-L sum           | 0.000 |     205 |
    |     26 | W sum               | 0.000 |     206 |
    |     27 | VA sum              | 0.000 |     207 |
    |     28 | VAR sum             | 0.000 |     208 |
    |     29 | PF sum              | 0.000 |     209 |
    | ******** Frequency *************************** |
    |     30 | Hz                  | 0.000 |     210 |
    | ******** Asymmetry *************************** |
    |     31 | Asymmetry L-N (%)   | 0.000 |     211 |
    |     32 | Asymmetry L-L (%)   | 0.000 |     212 |
    | ******** Demand ****************************** |
    |     33 | A L1 dmd            |   --- |     213 |
    |     34 | A L2 dmd            |   --- |     214 |
    |     35 | A L3 dmd            |   --- |     215 |
    |     36 | W L1 dmd            |   --- |     216 |
    |     37 | W L2 dmd            |   --- |     217 |
    |     38 | W L3 dmd            |   --- |     218 |
    |     39 | VA L1 dmd           |   --- |     219 |
    |     40 | VA L2 dmd           |   --- |     220 |
    |     41 | VA L3 dmd           |   --- |     221 |
    |     42 | W dmd               |   --- |     222 |
    |     43 | VA dmd              |   --- |     223 |
    | ******** Total Energy ************************ |
    |     44 | kWh tot.            |   --- |     224 |
    |     45 | KVARh tot.          |   --- |     225 |
    |     46 | KWh par.            |   --- |     226 |
    |     47 | KVARh par.          |   --- |     227 |
    | ******** Hours ******************************* |
    |     48 | Hours               |   --- |     228 |
    No archive data
    No events
    DLL           : KpModbus
    State         : error
    Comm. session : 20/04/2016 07:27:12
    | ******** Voltage ****************************************************************************** |
    |      1 | V L1-N              |                   -127,659,305,253,422,000,000,000.000 |     241 |
    |      2 | V L2-N              |                                                  0.000 |     242 |
    |      3 | V L3-N              |                                                  0.000 |     243 |
    |      4 | V L1-L2             |                                                  0.000 |     244 |
    |      5 | V L2-L3             |                                                  0.000 |     245 |
    |      6 | V L3-L1             |                                                  0.000 |     246 |
    | ******** Current ****************************************************************************** |
    |      7 | A L1                |                                                  0.000 |     247 |
    |      8 | A L2                |                                                  0.000 |     248 |
    |      9 | A L3                |                                                  0.000 |     249 |
    |     10 | A N                 |                                                  0.000 |     250 |
    | ******** Real Power (W) *********************************************************************** |
    |     11 | W L1                |                                                  0.000 |     251 |
    |     12 | W L2                |                                                  0.000 |     252 |
    |     13 | W L3                |                                                  0.000 |     253 |
    | ******** Apparent Power (VA) ****************************************************************** |
    |     14 | VA L1               |                       -219,365,394,444,938,000,000.000 |     254 |
    |     15 | VA L2               |                                                  0.000 |     255 |
    |     16 | VA L3               |                                                  0.000 |     256 |
    | ******** VAR ********************************************************************************** |
    |     17 | VAR L1              |         -1,488,065,280,206,370,000,000,000,000,000.000 |     257 |
    |     18 | VAR L2              |                                                  0.000 |     258 |
    |     19 | VAR L3              |                                                  0.000 |     259 |
    | ******** Phase Sequence *********************************************************************** |
    |     20 | Phase Sequence      |                                                  0.000 |     260 |
    | ******** Power Factor ************************************************************************* |
    |     21 | PF L1               | -9,730,282,549,430,550,000,000,000,000,000,000,000.000 |     261 |
    |     22 | PF L2               |                                                  0.000 |     262 |
    |     23 | PF L3               |                                                  0.000 |     263 |
    | ******** Sums ********************************************************************************* |
    |     24 | V L-N sum           |                    -58,516,990,333,482,500,000,000.000 |     264 |
    |     25 | V L-L sum           |                    -58,516,990,333,482,500,000,000.000 |     265 |
    |     26 | W sum               |                                                  0.000 |     266 |
    |     27 | VA sum              |                                                  0.000 |     267 |
    |     28 | VAR sum             |                                                    NaN |     268 |
    |     29 | PF sum              | -9,896,436,048,903,670,000,000,000,000,000,000,000.000 |     269 |
    | ******** Frequency **************************************************************************** |
    |     30 | Hz                  |                                                  0.000 |     270 |
    | ******** Asymmetry **************************************************************************** |
    |     31 | Asymmetry L-N (%)   |                                                  0.000 |     271 |
    |     32 | Asymmetry L-L (%)   |                                                  0.000 |     272 |
    | ******** Demand ******************************************************************************* |
    |     33 | A L1 dmd            |                                                    --- |     273 |
    |     34 | A L2 dmd            |                                                    --- |     274 |
    |     35 | A L3 dmd            |                                                    --- |     275 |
    |     36 | W L1 dmd            |                                                    --- |     276 |
    |     37 | W L2 dmd            |                                                    --- |     277 |
    |     38 | W L3 dmd            |                                                    --- |     278 |
    |     39 | VA L1 dmd           |                                                    --- |     279 |
    |     40 | VA L2 dmd           |                                                    --- |     280 |
    |     41 | VA L3 dmd           |                                                    --- |     281 |
    |     42 | W dmd               |                                                    --- |     282 |
    |     43 | VA dmd              |                                                    --- |     283 |
    | ******** Total Energy ************************************************************************* |
    |     44 | kWh tot.            |                                                    --- |     284 |
    |     45 | KVARh tot.          |                                                    --- |     285 |
    |     46 | KWh par.            |                                                    --- |     286 |
    |     47 | KVARh par.          |                                                    --- |     287 |
    | ******** Hours ******************************************************************************** |
    |     48 | Hours               |                                                    --- |     288 |
    No archive data
    No events