write integer with command

Forum Home Forums Communicating with Devices write integer with command

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #3706
    Charles Cool
    Participant

    I have been trying to modify a register in a PLC from RAPID SCADA. I can read the register with a dynamic text but when I click on it I do not get anything to input a number to modify the register.

    Could you explain the procedure to set this up?

    #3707
    Mikhail
    Moderator

    Hi,
    You should:
    1. Create an output channel in the configuration database.
    2. Specify the number of the output channel for a scheme component. And set the Action property of the component.
    3. Create a command in your Modbus template.

Viewing 2 posts - 1 through 2 (of 2 total)