Forum Home › Forums › Communicating with Devices › Modbus › Siemens Logo! Modbus
- This topic has 16 replies, 4 voices, and was last updated 8 years ago by
Mikhail.
-
AuthorPosts
-
July 4, 2018 at 3:04 am #3960
mkieffer
ParticipantI am trying to setup Modbus to a Logo! 0BA0 device
I have the Communication line setup in communicator, Rapid SCADA will connect to the PLC as a (shows server connected on the PLC) however I cannot read from any network inputs or write to a network output to the PLC.
Does anyone have a template made for the LOGO! series?
July 4, 2018 at 10:33 am #3961
manjey73ParticipantYou have a table of registers from the manufacturer Logo! ?
Status of inputs and outputs.
Plus, the other registers you create yourself in the program Logo! and there should be a register card after its programming.July 5, 2018 at 12:48 am #3962mkieffer
ParticipantI will clarify the manufacture of the device is Siemens the product series is called LOGO!
As per the PLC guide the Modbus addressing is as follows
I am able to get RapidSCADA connected (showing connected as server on the PLC) I am able to read inputs/outputs (I&Q) from the PLC
Please see the following capture form the PLC programming application.

The trouble starts if I try and send command 1 which is to enable 8193 (Q1) nothing happens, if I send command 2 it will enable Q2 not problem.


The next issue I also cannot enable the network input NI1, send command 3 and nothing happens

Here are the screenshots from the modbus line configuration from RapidSCADA
Comm_Line_Param

Any assistance would be great! I’ve been spending a lot of hours trying to solve this and would really like to use RapidSCADA.
July 5, 2018 at 6:11 am #3963
manjey73Participantc Q2 you have no problem because it is not yet tied to the program. Q1 may not be enabled due to overwriting in the program. Now there is no Logo at hand! Soft Comfort to understand.
As for the lack of response to the NI1 input, a possible problem is that the Communicator sends to the double device,and the input user variables you have are word. The formula for rearranging the bytes before sending the command.
-
This reply was modified 8 years, 3 months ago by
manjey73.
July 5, 2018 at 7:20 am #3965
manjey73ParticipantIn response, the device says that it has included the network variable NI1, so most likely at the program level it is not included.
July 5, 2018 at 4:10 pm #3966
MikhailModeratorHi,
According to the communication line log, the device understands your command. Nothing happens because of a device logic. You should check that you specify the correct address and value of the commands.
Does the manufacturer provide an utility application that can send the required commands to compare data packages?July 6, 2018 at 3:39 pm #3971mkieffer
ParticipantI am not aware of any utilities, I did find another manual that goes into more detail about network connections using modbus. I will check through it and see what I can find/test.
July 7, 2018 at 12:23 pm #3972
MikhailModeratorYou may contact the Logo support, provide them communication log and ask for explanation about the device behaviour.
October 22, 2018 at 10:56 am #4458
Hennie_KotzeParticipantMkieffer,
I am working on the same PLC at the moment.
Did you manage to get your system working?
Would you mind collaborating with me via email so i can learn how you configured your software please?
Hennie Kotze
hennie _aty_ kwenamining.co.za
+27794914321 (south africa)Regards,
-
This reply was modified 8 years ago by
Mikhail.
October 23, 2018 at 6:15 am #4465
Hennie_KotzeParticipantMkieffer,
Can you please share some screenshots of your PLC setup (Network project) and settings, as well as your rapid scada settings?
I’m still struggling to get connection between the two…
October 23, 2018 at 10:33 am #4466mkieffer
ParticipantHi Hennie,
I ended up abandoning Rapid SCADA, I was unable to get it to properly communicate with the PLC.
MK
October 23, 2018 at 11:17 am #4467
Hennie_KotzeParticipantMK,
Sorry to hear that….
Did you find an alternative?? I would also like to explore different options…
I managed to get my communication working, but now i’m struggling with the graphics in the web station…
HK
October 23, 2018 at 2:34 pm #4468
MikhailModeratorHennie, you may try the above recommendations.
October 23, 2018 at 3:44 pm #4473mkieffer
ParticipantHennie,
I ended up going to — haven’t had a chance to get back to working on my project with it yet though. It’s far more complex than Rapid SCADA.
Would you mind sharing how you got the communication working with Rapid SCADA? It would be much appreciated!
Mike
-
This reply was modified 8 years ago by
Mikhail.
October 23, 2018 at 5:07 pm #4474
Hennie_KotzeParticipantMikhail,
What recommendations are you referring to?
MK,
I will send a compilation of screenshots of all my settings, on the scada and on the PLC. I’m in South Africa (GMT +2) so we are going to bed now. Will send them in the morning.
From what i can see in your initial question, you are trying to send a command from the scada to the PLC via network input. Now i have used these network inputs and outputs successfully between two PLC’S, but i think you should maybe send your command via memory address (M) in the PLC. In your modbus address screen shot you’ll see they are mapped as coil 8257. They are read / write (RW). So instead of using the NI1, just use coil 8257 and in the PLC that will be M1.
I will try that tomorrow and let you know.
From where are you?
-
This reply was modified 8 years, 3 months ago by
-
AuthorPosts
- You must be logged in to reply to this topic.