Read communication status – MODBUS TCP

Forum Home Forums Communicating with Devices Modbus Read communication status – MODBUS TCP

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #3565
    Marko
    Participant

    Hello,

    Is there any way to read communication status from modbus TCP device as
    input channel in rapid scada?

    I see communication status in communicator, is it possible to show that status as input channel?

    Also i need that as a trigger to send email as notification that we lost communication with that device (as watchdog).

    #3586
    Mikhail
    Moderator

    Hi,
    Yes. Add new input channel of the Calculated type and use the formula:
    Stat(1) > 0 ? 1 : 0
    where 1 is the input channel number of any tag.

    To send notifications you need Automatic Control Module, see http://doc.rapidscada.net/content/en/modules/mod-auto-control.html

Viewing 2 posts - 1 through 2 (of 2 total)