OPC write value issue-IBH opc server

Forum Home Forums Communicating with Devices OPC OPC write value issue-IBH opc server

This topic contains 97 replies, has 3 voices, and was last updated by Mikhail Mikhail 2 months, 2 weeks ago.

Viewing 15 posts - 16 through 30 (of 98 total)
  • Author
    Posts
  • #4353
    Avatar
    mariodavid
    Participant

    the manufacturer wrote: “I would think that installing the OPC Foundation OPC Analyzer as a go-between between Rapdid Scada and the Server would give them all the information that is needed”.

    How can i get the OPC analizer?

    #4357
    Mikhail
    Mikhail
    Moderator

    Me and Google have no idea. I found this free tool that may be useful.

    #4358
    Mikhail
    Mikhail
    Moderator
    #4373
    Avatar
    mariodavid
    Participant

    I use opc analyzer with quick ckient and rapid scada. this is the log.

    first, quick client:

    “OPC Analyzer Trace – Application Version 1.2.1012
    saved on mar 9. oct 12:09:15 2018

    12:08:35.437 – IOPCSyncIO::Write —————————————————————-
    General:
    GroupName: PLC1.Generic
    GroupServerHandle: 0x5721688
    HRESULT: 0x00000000 S_OK

    In Parameters:
    pItemValues:
    [000] VT_BOOL -1
    dwCount: 1
    phServer:
    [000] 0x06895348

    Out Parameters:
    ppErrors:
    [000] 0x00000000 S_OK

    12:08:35.967 – IOPCDataCallback::OnDataChange —————————————————
    General:
    HRESULT: 0x00000000 S_OK
    GroupName: GRP06897320
    numCallbacks: 10
    minTime: 54.974 ms
    averageTime: 134.769 ms
    GroupServerHandle: 0x302398
    maxTime: 508.228 ms
    CallTime: 101.790 ms

    In Parameters:
    hrMasterquality: 0x00000000 S_OK
    pvValues:
    [000] VT_BOOL -1
    [001] VT_BOOL -1
    [002] VT_BOOL -1
    dwCount: 3
    hrMastererror: 0x00000000 S_OK
    pftTimeStamps:
    [000] 2018-10-09T16:08:35.608
    [001] 2018-10-09T16:08:35.718
    [002] 2018-10-09T16:08:35.718
    dwTransid: 0
    phClientItems:
    [000] 0x00000008 [001] 0x0000000b [002] 0x00000013
    hGroup: 0x0
    pwQualities:
    [000] 0x00c0 OPC_QUALITY_GOOD
    ::::
    [002] 0x00c0 OPC_QUALITY_GOOD
    pErrors:
    [000] 0x00000000 S_OK
    ::::
    [002] 0x00000000 S_OK

    12:08:36.014 – IOPCDataCallback::OnDataChange —————————————————
    General:
    HRESULT: 0x00000000 S_OK
    GroupName: PLC1.Generic
    numCallbacks: 11
    minTime: 0.139 ms
    averageTime: 0.429 ms
    GroupServerHandle: 0x5721688
    maxTime: 2.238 ms
    CallTime: 0.192 ms

    In Parameters:
    hrMasterquality: 0x00000000 S_OK
    pvValues:
    [000] VT_BOOL -1
    [001] VT_BOOL -1
    [002] VT_BOOL -1
    dwCount: 3
    hrMastererror: 0x00000000 S_OK
    pftTimeStamps:
    [000] 2018-10-09T16:08:35.718
    [001] 2018-10-09T16:08:35.608
    [002] 2018-10-09T16:08:35.718
    dwTransid: 0
    phClientItems:
    [000] 0x003d4608 [001] 0x003d42f8 [002] 0x003d4138
    hGroup: 0x3e2fe8
    pwQualities:
    [000] 0x00c0 OPC_QUALITY_GOOD
    ::::
    [002] 0x00c0 OPC_QUALITY_GOOD
    pErrors:
    [000] 0x00000000 S_OK
    ::::
    [002] 0x00000000 S_OK

    12:08:39.009 – IOPCDataCallback::OnDataChange —————————————————
    General:
    HRESULT: 0x00000000 S_OK
    GroupName: GRP06897320
    numCallbacks: 11
    minTime: 54.974 ms
    averageTime: 132.910 ms
    GroupServerHandle: 0x302398
    maxTime: 508.228 ms
    CallTime: 114.316 ms

    In Parameters:
    hrMasterquality: 0x00000000 S_OK
    pvValues:
    [000] VT_BOOL -1
    [001] VT_BOOL 0
    dwCount: 2
    hrMastererror: 0x00000000 S_OK
    pftTimeStamps:
    [000] 2018-10-09T16:08:38.588
    [001] 2018-10-09T16:08:38.588
    dwTransid: 0
    phClientItems:
    [000] 0x00000004 [001] 0x00000008
    hGroup: 0x0
    pwQualities:
    [000] 0x00c0 OPC_QUALITY_GOOD
    [001] 0x00c0 OPC_QUALITY_GOOD
    pErrors:
    [000] 0x00000000 S_OK
    [001] 0x00000000 S_OK

    12:08:39.040 – IOPCDataCallback::OnDataChange —————————————————
    General:
    HRESULT: 0x00000000 S_OK
    GroupName: PLC1.Generic
    numCallbacks: 12
    minTime: 0.139 ms
    averageTime: 0.407 ms
    GroupServerHandle: 0x5721688
    maxTime: 2.238 ms
    CallTime: 0.159 ms

    In Parameters:
    hrMasterquality: 0x00000000 S_OK
    pvValues:
    [000] VT_BOOL -1
    [001] VT_BOOL 0
    dwCount: 2
    hrMastererror: 0x00000000 S_OK
    pftTimeStamps:
    [000] 2018-10-09T16:08:38.588
    [001] 2018-10-09T16:08:38.588
    dwTransid: 0
    phClientItems:
    [000] 0x003d44b8 [001] 0x003d42f8
    hGroup: 0x3e2fe8
    pwQualities:
    [000] 0x00c0 OPC_QUALITY_GOOD
    [001] 0x00c0 OPC_QUALITY_GOOD
    pErrors:
    [000] 0x00000000 S_OK
    [001] 0x00000000 S_OK”

    rapid scada:

    “OPC Analyzer Trace – Application Version 1.2.1012
    saved on mar 9. oct 12:11:09 2018

    12:10:15.964 – IOPCItemIO::WriteVQT ————————————————————-
    General:
    HRESULT: 0x00000000 S_OK

    In Parameters:
    pszItemIDs:
    [0] = PLC1.Generic.bandera_ESB
    dwCount: 1
    pItemVQT:
    Item 0:
    vDataValue = VT_BOOL -1
    bQualitySpecified = FALSE
    wQuality = 0x0000 OPC_QUALITY_BAD
    bTimeStampSpecified = FALSE
    ftTimeStamp = 1601-01-01T00:00:00.000

    Out Parameters:
    ppErrors:
    [000] 0x00000000 S_OK”

    #4392
    Mikhail
    Mikhail
    Moderator

    We can see the difference:

    In the 1st example:
    IOPCSyncIO::Write

    In the 2nd example:
    IOPCItemIO::WriteVQT

    Can you ask the OPC server developer if they support IOPCItemIO::WriteVQT?

    #4404
    Avatar
    mariodavid
    Participant

    developer wrote: Hello Mario,

    “The issue here is that the WriteVQT is writing a value of -1 (high) and a quality of Bad. Where the Quick Client write is only writing a -1 (high). Your other client needs to not write the quality bad if you want the quality to remain good and the write succeed.

    Why is the rapid scada writing a bad quality? OPC Specs declare that the value is undefined if OPC quality is bad, so the server is not processing the write.

    Thanks,
    Marc”

    #4405
    Avatar
    mariodavid
    Participant

    developer wrote: Hello Mario,

    “The issue here is that the WriteVQT is writing a value of -1 (high) and a quality of Bad. Where the Quick Client write is only writing a -1 (high). Your other client needs to not write the quality bad if you want the quality to remain good and the write succeed.

    Why is the rapid scada writing a bad quality? OPC Specs declare that the value is undefined if OPC quality is bad, so the server is not processing the write.

    Thanks,
    Marc”

    #4406
    Avatar
    mariodavid
    Participant

    Will there be any difference if I use the 5.5.3 version? I am using 5.5.2 rapid scada version.

    #4410
    Mikhail
    Mikhail
    Moderator

    As I understand, quality is not specified.
    Item 0:
    vDataValue = VT_BOOL -1
    bQualitySpecified = FALSE
    wQuality = 0x0000 OPC_QUALITY_BAD

    #4411
    Mikhail
    Mikhail
    Moderator

    5.5.3 version? I am using 5.5.2

    The OPC driver was not changed.

    #4413
    Mikhail
    Mikhail
    Moderator

    Please ask Marc why he doesn’t take into account the QualitySpecified field?
    Mario, I’m interested in solving this issue. Let’s continue the dialog.

    #4443
    Avatar
    mariodavid
    Participant

    Hi. The developer does not answer yet. I have been searching and some servers are not compatible with writeVQT method. https://advosol.com/manuals/opcdanet/topic177.html

    Is there the possibility of writing with another method?

    #4444
    Mikhail
    Mikhail
    Moderator

    Hi,

    Try switch to OPC DA 2 in Communicator and check what write command is used.

    I can set Quality in the driver, but before I do it, it’s better to hear an answer from the OPC server developer.

    #4446
    Avatar
    mariodavid
    Participant

    Hello.

    I try with 2.XX and and the same thing happens. Marc:

    “Hello Mario,

    I have been able to install rapid scada and am currently testing this on our system. I am having some trouble issuing a write – how are you doing that exactly on your end?

    The reason I do not think this is an issue with the IBH server is that it actually responds with a “success” so I would expect that the write has been processed correctly – this is something I would like to see here on my end.

    Kind Regards,

    Marc”

    Is it possible to write with IOPCSyncIO::Write?

    #4451
    Mikhail
    Mikhail
    Moderator

    Is it possible to write with IOPCSyncIO::Write?

    I don’t think that this is possible.
    In the source code of KpOpc.dll driver I just use daServer.Write(new Opc.Da.ItemValue[] { itemVal }); and the library made by OPC Foundation choose lo-level method WriteVQT.

    I can try setting Quality field of the item being written.