opc on network

Forum Home Forums Communicating with Devices OPC opc on network

Viewing 15 posts - 1 through 15 (of 17 total)
  • Author
    Posts
  • #654
    mails2saurabh
    Participant

    How do I connect to opc server on network to take data in rapid scada??

    #656
    Mikhail
    Moderator

    You can install SCADA-Communicator on the PC where OPC server is installed.

    #657
    mails2saurabh
    Participant

    How will scada server / scada web will communicate to scada communicator service on network??

    #658
    Mikhail
    Moderator

    Just set server IP address or host name in Common Parameters tab in SCADA-Communicator. They communicate via TCP.

    #659
    mails2saurabh
    Participant

    Ok,I will come back after checking ?

    #745
    mails2saurabh
    Participant

    As suggested, I installed scada communicator on the opc server, I am not able to browse the opc server. I changed ip address,in the common parameters in the server option. But I am getting following error when importing communication lines.
    “error connecting to scada server: A connection attempt failed because the connects party did not respond after a period of time, or a established connection failed because connected host failed to respond 172.16.0.3:10000.”

    Please suggest.

    #746
    Mikhail
    Moderator

    Browse OPC Server via UI of SCADA-Communicator doesn’t depends on connection with SCADA-Server. What error message appears?
    You have to allow incoming TCP connection through 10000 port on a firewall on a PC where SCADA-Server installed.

    #749
    mails2saurabh
    Participant

    Thanks, I am able to open the web interface on the network, but I am not able to login using user: admin , password: 12345.
    However, with the same user name and password , I am able to login on the localhost. Help !!

    #750
    mails2saurabh
    Participant

    I m presently in front of system…

    #751
    mails2saurabh
    Participant

    Error is – Unable to login: Server is unavailable. Used port in 80

    #752
    mails2saurabh
    Participant

    After rebooting localhost, I am not able to login on localhost also..

    #753
    mails2saurabh
    Participant

    Error code on,ScadaServerSvc
    Error start communication with,client: An attempt was made to access socket in a way forbidden by its access permission.

    This error started, after I made changes to , user name password and port no., changed to 80, made all usernames: admin on the interface.

    Suggest!! What needs to be corrected??

    #754
    Mikhail
    Moderator

    SCADA-Web connects to SCADA-Server using TCP port 10000. Check the connection settings with SCADA-Web Configurator utility.
    Port 80 is used by IIS. I should not use it for other purposes.

    #756
    mails2saurabh
    Participant

    But using port 10000, I was not able to connect to scada server,on a network machine using internet explorer. Using port 80 , I could connect, any how , I will check this to open on local host first !!

    #763
    Mikhail
    Moderator

    Did you tried opening port 10000 on a firewall?
    Port 80 is busy that is why you cant use it for SCADA-Server.

Viewing 15 posts - 1 through 15 (of 17 total)