Forum Home › Forums › Understanding the Software › How to setup Event
- This topic has 11 replies, 5 voices, and was last updated 1 year ago by Mikhail.
-
AuthorPosts
-
April 20, 2018 at 2:31 pm #3566MarkoParticipant
Hello,
How to setup event when you have discrete or calculated discrete input channel?
What should we setup so event show up?In mine case i am using calculated discrete because i have formula that extract
one bit from integer.April 23, 2018 at 6:45 am #3588MikhailModeratorHi,
For the input channel, tick the “Write events” and “Event on change” check boxes. Don’t forget to pass the configuration to Server and restart the Server service.
April 23, 2018 at 7:53 am #3591MarkoParticipantHi,
This is working but i notice SCADA making event when status changed. From OFF to ON or ON to OFF.
What should we do if we want to make event only when status go from OFF to ON?
I want to use event trigger in automatic control module to send some email that give notification to user that something is in alarm status. In this case i want to send email when discrete channel is in true status and not send email when discrete channel go back to false status.April 23, 2018 at 2:06 pm #3600MikhailModeratorHi,
You can create a trigger only for OFF-ON transition. Make sure that your version of the module is up to date (5.2.2.0).August 29, 2019 at 12:00 am #5887HoracioParticipantHello,
How do I create an event that triggers on OFF-ON transition?
(Administrator version 5.5.0.0)Thank you
August 29, 2019 at 2:35 pm #5890MikhailModeratorHello,
You should open the Input Channels table and tick the checkboxes of the appropriate channels: Write Events, Event on Change.December 17, 2019 at 7:49 pm #6206SGGParticipantHello
i am unable to acknowledge an event.
i tried using my own project and also the demo project…but the same thing. it does not change from No to Yes. The screen shot of the server log is shown below.
https://drive.google.com/open?id=1q3Jlhg2QycjtflW00C04L1xWItHAhfHp
Please help me resolve this issue.
Also, can i flip the arrangement of the events such that the most current event will be at the top and not at the bottom?
Thanks
December 18, 2019 at 10:58 am #6208SGGParticipantHello,
i tried acknowledging the event again after like 12 hrs and it worked, i guess it was an error somewhere on my path.But How do i flip the events such that the most current event is at the top.
Thanks.
December 18, 2019 at 3:56 pm #6214MikhailModeratorHow do i flip the events such that the most current event is at the top.
The event table automatically scrolls down when new event added if you don’t touch the table for some time.
March 29, 2023 at 4:08 pm #12322TDEParticipantHi,
How can use auto control module (please mention the steps) to create an event of changing the status of Boolean tags and after 5 seconds it returns to the old status.
Cordially
March 30, 2023 at 8:34 am #12329MikhailModeratorHi,
Automatic Control Module sends commands, but it does not create events.
Event is generated if a channel value or status change if event flags are specified.
May be you should create a channel formula to change it as needed, and events will be generated.March 30, 2023 at 8:35 am #12330MikhailModeratorAlso you can use Automatic Control Module to send commands that change channel value and status, that will cause new events.
-