Dynamic Alarm Values (Set by User/Operator)

Forum Home Forums Understanding the Software Dynamic Alarm Values (Set by User/Operator)

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #3596
    jacklondon
    Participant

    Hi

    is it possible to let the user edit/change the alarm levels dynamically at the web frontend and then set them accordingly in the corresponding input channels’ alarm limits (by a formula for example)?

    Regards

    • This topic was modified 5 years, 11 months ago by jacklondon.
    #3601
    Mikhail
    Moderator

    Hi,
    Yes. You can create input channels that describe alarm levels and calculate statuses of the controlled channels using formulas.
    Also you need output channels to be able to change levels. You can do it by the formula SetVal of an output channel. See http://doc.rapidscada.net/content/en/software-configuration/using-formulas.html