Current Data sudden become Not Ready

Forum Home Forums Runtime Bugs Current Data sudden become Not Ready

Viewing 6 posts - 16 through 21 (of 21 total)
  • Author
    Posts
  • #14239
    kcks66
    Participant

    Hi Mikhail,

    Pls advice for if I configure Automatic (Delayed Start) for Rapid SCADA’s services? Do you think if I delayed the Rapid SCADA from start running for 1 ~ 2 minutes after PC restart can solve the problem?

    https://ibb.co/T2NSq4d

    Thank you.

    #14242
    Mikhail
    Moderator

    Hi,

    It can be a good idea. Please let us know if it helps to solve the issue.

    #14247
    kcks66
    Participant

    Hi Mikhail,

    Today I purposely tripped the PC power supply and later resumed power supply. I can see Rapid SCADA instance Server and Communicator services status Starting and then Normal.

    I checked Achieve status is all Ready, and data is writing into PostgreSQL database normally.

    I will continue monitor until next PC actual sudden shutdown happen and update here.

    #14257
    Mikhail
    Moderator

    Thank you.

    #14293
    kcks66
    Participant

    Hi Mikhail,

    Today the PC encountered actual power supply tripped. The PC auto resume after around 30 minutes later. I checked Rapid SCADA and everything is working well.

    I think the Automatic (Delayed Start) setting worked.

    #14298
    Mikhail
    Moderator

    That’s good! Thank you for the info.