September 9, 2020 at 9:12 am #7245
kcks66
ParticipantHi Mikhail,
I have installed Chart Pro and extracted them to the directories. Changed the Chart Plugin to Chart Pro, saved and downloaded into Project. I get this error:
Application Error
An application error occurred. If it repeats often, please contact the support.
Details:
Method not found: ‘!!0 Scada.Web.WebUtils.GetParamAsEnum(System.Collections.Specialized.NameValueCollection, System.String, !!0)’.Webstation 5.1.0.0
Chart Pro 5.1.0.0Is there any steps that I missed?
Thank you.September 9, 2020 at 12:35 pm #7246Mikhail
ModeratorHi,
This error caused by version mismatch.
You have the latest Chart Pro, but Webstation looks outdated.Could you check the timestamp of C:\SCADA\ScadaWeb\bin\ScadaWebCommon.dll file?
We have a minor bug that after updating Webstation, it’s version number still 5.1.0.0. That’s why it’s better to check file age.September 10, 2020 at 1:43 am #7247kcks66
ParticipantHi Mikhail,
My PC ScadaWebCommon.dll timestamp is 2020/1/28.
September 10, 2020 at 12:52 pm #7251Mikhail
ModeratorYou should update Rapid SCADA to version 5.8.1 to fix this issue.
September 11, 2020 at 8:28 am #7256kcks66
ParticipantHi Mikhail,
I update Rapid SCADA to version 5.8.1. However, I still got error:
Application Error
An application error occurred. If it repeats often, please contact the support.
Details:
The specified string is not array of integers.September 11, 2020 at 3:23 pm #7257Mikhail
ModeratorHi,
Try clearing browser cache. If it doesn’t help, please provide a link to a screenshot with the error.
September 12, 2020 at 1:29 am #7261kcks66
ParticipantHi Mikhail,
The chart is working well now after cleared browser cache.
Thank you.April 8, 2021 at 11:53 am #8673hethongscada62
ParticipantDear Mr.Mikhail,
The registration key for Chart Pro was configured. That seems is working in Web well. But the software have not processed the Chart.
https://ibb.co/19ZFhpg
https://ibb.co/J72mskk
Could you let me know where is wrong? Where can i check?
Thanks and best regards
From Han HoangApril 8, 2021 at 1:32 pm #8674hethongscada62
ParticipantDear Mr.Mikhail,
The registration key for Chart Pro was configured. That seems is working in Web well.
https://ibb.co/Zm08Msv
But the software have not processed the Chart.
https://ibb.co/fYKCdgr
Could you let me know where is wrong? Where can i check?
Thanks and best regards
From Han HoangApril 8, 2021 at 2:34 pm #8675Mikhail
ModeratorHello,
You need to select Chart Pro in the configuration of the web application.April 9, 2021 at 1:08 am #8681hethongscada62
ParticipantHello Mr.Mikhail,
Yes, all keys were selected in the configuration of the web application.
https://ibb.co/T4q9p6q
ThanksApril 9, 2021 at 1:07 pm #8692Mikhail
ModeratorHello,
In web browser open http://localhost/scada/plugins/Config/WebConfig.aspx, select “Chart plugin”, save configuration and download it into the project as written in the manual.April 13, 2021 at 12:11 pm #8720hethongscada62
ParticipantDear Mr.Mikhail,
Chart Pro Plugin was selected, but can not get the result.
Some screenShot are following:
https://ibb.co/DktzQTb
https://ibb.co/SQmYbTH
https://ibb.co/M2j2v3T
Where is wrong?
Where have i check?
Thanks and best regardsApril 13, 2021 at 3:25 pm #8721Mikhail
ModeratorHello,
You should provide write access to the configuration directory and configuration file:
C:\SCADA\ScadaWeb\config\
C:\SCADA\ScadaWeb\config\WebSettings.xmlor
/opt/scada/ScadaWeb/config/
/opt/scada/ScadaWeb/config/WebSettings.xmlApril 13, 2021 at 3:27 pm #8722Mikhail
ModeratorIf you already did it, repeat.
-