Automatic Control Module integration

Forum Home Forums Understanding the Software Automatic Control Module integration

Viewing 8 posts - 31 through 38 (of 38 total)
  • Author
    Posts
  • #7711
    Mikhail
    Moderator

    Hello,

    I suggest configuring the Rapid SCADA on Windows and then upload it to Linux. You should create a new deployment profile in Administrator to connect to remote machine.

    #7750
    hethongscada62
    Participant

    Dear Mr.Mikhail,
    The Module auto control was activated. The first I am using a trial key on Windows, then it will be uploaded to Raspberry Pi4. So Could you let me know step by step to configure to send a release command?
    Thanks and best regards
    Han Hoang

    #7752
    Mikhail
    Moderator

    Dear Han,

    Could you let me know step by step to configure to send a release command?

    Please explain your question. What is “release command”?

    #7754
    hethongscada62
    Participant

    Dear Mr.Mikhail,
    On topic” Send command” i asked you this question: “That means Press the Button, the value will be 1, released the Button, past some second, the value auto will be 0. I do likes that, don’t i?
    You answered that: “I also would choose this method.
    When a user click the button, the 1st command is sent. Then you need Automatic Control Module that triggers on the 1st command and automatically sends the 2nd command after the specified delay.”
    Thanks

    #7757
    Mikhail
    Moderator

    Hello,

    You need to create a command trigger in the module settings. Under this trigger create a command to send “release command”. If you provide screenshots of the settings, I can check them.

    #7760
    hethongscada62
    Participant

    Dear Mr.Mikhail,
    This is a screenshot.
    https://ibb.co/1GvP2T4
    Thanks
    Han Hoang

    #7769
    Mikhail
    Moderator

    Hello,

    Check the command type of the trigger (standard or binary).

    To avoid infinite loop:
    1. You need to create another output channel for the 2nd command.
    2. Or check the command value in the trigger.

    #7791
    hethongscada62
    Participant

    Dear Mr.Mikhail,
    The problem was resolved.
    Thank you very much.
    Han Hoang