  • #16475
    odobrev
    Participant

    @oley Oh and also, pay attention to Smart Logger ACL Security.

    In Smart Logger Modbus TCP settings, you either need to disable ACLs or add your IP adresses to Client list (limited to 5 in Smart Logger 3000).


    Link setting : Enable (limited)
    Client 1 Ip Address : Your SCADA PC or Server IP
    Address mode : Communication address
    Logger address : 10

    At least these settings work for me.

    • This reply was modified 2 months, 2 weeks ago by odobrev.
    #16477
    odobrev
    Participant

    Also be aware that Smart Logger has a dynamic mapping by inverter that needs to be calculated from the inverter modbus starting address.

    It’s in the documentation.

    I had 3 inverters starting from 12 so my config file is based on this.

    #16478
    oley
    Participant

    @odobrev
    Thanks again!

    Unfortunately I can not establish the connection with an error in line log: “No connection could be made because the target machine actively refused it”.

    Probably some network setting are wrong. I am doing it on fresh Windows 11 VM, firewall is completely disabled. Adresses are ok, I can ping and log in via browser into logger interface.

    I tried Modbus TCP settings with Link setting Limited and IP address as you mentioned also with unlimited access.

    What are your Modbus TCP settings on the logger?
    Address mode Logical/communication address
    Logger address
    Fast scheduling

    Do you use LAN or WAN port on the logger?

    #16479
    odobrev
    Participant

    @oley

    I did not configure the logger myself but from what is configured in my interface in Wired Network is :

    — Wired Network
    WAN/LAN port working mode : WAN+LAN

    — WAN & SFP Port Parameters
    DHCP : Disable
    All static IP fields and dns are set with the IP I’m using to connect to the logger.

    — LAN Port parameters
    Static IP set to some unknown IP that I’m not using and the cable is not pugged in.

    As for Modbus TCP settings, I already mentionned it before :

    Link setting : Enable (limited)
    Client 1 Ip Address : Your SCADA PC or Server IP
    Address mode : Communication address
    Logger address : 10

    As for settings in rapid scada communicator, you have it all in github screenshots folder.

    #16480
    oley
    Participant

    @odobrev

    Got it!

    It was the LAN port. I have used the second one for the connection.
    After replacement of the port I can connect.

    Thank you for your help!

    #16481
    odobrev
    Participant

    @oley

    Glad I could help you.

    Don’t hesitate if you need more info.

    Now you’re in the fun part, adapting register configuration to your needs, testing and UI implementation…

    Took me two weeks because their documentation often mentions registers that are not readable depending on your configuration or system.
    The sad part is that not everything is available in the MODBUS Interface of the Logger, you’re short of a lot of detailed variables that you get from directly using Inverter Modbus Interface. If I had a choice, I would’ve used another generic gateway such as Moxa branded ones (they’re fantastic) for each inverter to get all the variables.

    #16482
    Mikhail
    Moderator

    > Not sure if there are rules for file sharing links on this forum (I did not find a policy)
    Links are allowed if they are on-topic, excluding links to other SCADA.