Modbus TCP Server
Forum Home › Forums › Communicating with Devices › Modbus › Modbus TCP Server
Viewing 15 posts - 1 through 15 (of 19 total)
  • #5571
    burscheservas
    Hi all,
    I try to connect rapidscada directly to a PLC using Modbus TCP. The PLC has the libmodbus library implmented to establish the modbus connection.
    The PLC can communicate with test software and also with the Modbus simulator (plcsimulator.org).
    On the rapidscada side, I have been able to manage the connection from rapidscada to the Modbus Simulator as well. It works in principle.
    If I add a new communication line with new object to the rapidscada configuration and set the communication to Modbus TCP Server (TcpPort = 502, behavior = slave, connmode = shared, devselmode = byipaddress) the connection can not be established.
    I tried all possible combinations, but the tcpport 502 is not opening.
    It seems that the TCP Server is not running correctly.
    Do you have any idea/advice how to go forward to check the issue?
    Thanks in advance.
    Regards,
    John
    #5574
    Rapid SCADA works as TCP client, not TCP server. It connects to a PLC which is TCP server and PLC keeps port 502 open.
    #5580
    burscheservas
    Hi Mikhail,
    Thanks for the quick response!
    This is unfortunately not good to hear for me.
    Do you know maybe any stand alone Modbus TCP server software (open source / freeware) that can be used as software modbus TCP coupler?
    regards,
    John
    #5587
    Hi John,
    I researched for this, and I have’t found any free solution. We can develop such driver as a custom development by a contract.
    #5595
    burscheservas
    Hi Mikhail,
    Thanks for your reply and your offer.
    Currently, I am investigating my options. Should I come to the requirement to use a customized solution I will come back to you.
    Regards,
    John
    #5599
    Hi John,
    Sure. Any time. We provide high quality and competitive price 🙂
    #6052
    Krzysztof
    Helo
    I have a problem with communication with the slave simulator.
    I can’t ask him for more than 127 registers. It does not appear to have such a limitation. Is there any restriction on Rapid Scada or modbus driver?
    #6054
    Like this limitation of the Protocol on 256 bytes when using standard reading functions
    #6058
    Too big packets are not reliable. If you face limits in Modbus Template Editor, this is because of the Modbus standard.
    #6062
    Krzysztof
    thx guys
    #14144
    mauricio
    Hello, I have version 6.2.0.0 installed in Windows 10
    I made a test project with modbus TCP
    When starting the connection, it correctly makes the first 76 queries and then the communication fails.
    ++++++++  LINE LOG +++++++++++++++++++++++++
    2024-03-06 15:02:26 Session with the device [1] Gen1
    Request element group "FactEscG1"
    Send (12): 00 49 00 00 00 06 01 03 C3 50 00 03
    Receive (7/7): 00 49 00 00 00 09 01
    Receive (8/8): 03 06 13 92 00 03 00 00
    OK
    Send (12): 00 4A 00 00 00 06 01 03 C3 50 00 03
    Receive (7/7): 00 4A 00 00 00 09 01
    OK
    Send (12): 00 4B 00 00 00 06 01 03 C3 50 00 03
    Receive (7/7): 00 4B 00 00 00 09 01
    OK
    2024-03-06 15:02:27 Session with the device [1] Gen1
    Send (12): 00 4C 00 00 00 06 01 03 C3 50 00 03
    Receive (7/7): 00 4C 00 00 00 09 01
    OK
    Send (12): 00 4D 00 00 00 06 01 03 C3 50 00 03
    Receive (0/7):
    Error: communication failed
    Send (12): 00 4E 00 00 00 06 01 03 C3 50 00 03
    Receive (0/7):
    Error: communication failed</strong></blockquote>
    ++++++++ END  LINE LOG +++++++++++++++++++++++++
    When applying restart line it again correctly does the first 76 queries and then communication fails.
    The TCP server used works well with other scada software.
    Please indicate steps to follow to solve the problem.
    #14155
    In case of communication error, the driver should reconnect. What messages do you get after the error in the log?
    Also consider increasing the timeout and delay parameters in the device properties in Communicator.
    #14518
    ibrahim eren
    I am a new user of Rapid SCADA and would like to use your product. However, I have been unable to run Rapid SCADA as a TCP Server. We have 4G modems operating as TCP Clients at various field points, and behind these modems, we have Modbus RTU devices. I want to access these devices through Rapid SCADA and read their registers. Unfortunately, even though Rapid SCADA claims to be listening on port 502 as a TCP Server, it does not appear to be doing so. I need your assistance.
    ibrahim eren
    #14519
    Hello Ibrahim,
    Please provide screenshots of the Communicator settings and the communication line log.
    Make sure that the modems are configured to initiate a connection to the TCP server.
    #14520
    Also try to connect to Communicator by any TCP client utility. You should see that a connection is established.