    Hello
    I am new to this, and would need some more help: I try to read a device using modbus TCP. I can ping the device, but cannot read any registers from it. Whatever I try, I get Error: Communication Failed message in the Line Log/Stat. With localhost + ModbusSimulator the project is working, but as soon I try to connect to this device, I got error. I read it somewhere here in another topic/comment that the Byte Order can affect this..? Or it has nothing to do with Communication errors.. I tried many things: connected directly, disabled firewall, and yes – watched the modbus videos, etc.
    Any advice would be appreciated. Will upload photos and logs tomorrow. Thanks, Gabor

    #17817
    manjey73
    Participant

    If you don’t see any bytes transmitted from the device in the log, then there is a problem with the connection.

    #17818
    Gabor
    Participant

    Thank you for your reply. This is what I am thinking too.. Unfortunately can’t figure it out what the problem can be. Changed the IP address from localhost to the device IP in the project file (in 2 places), is there anything else to do? Target Device responses to ping and also tested port 502 with telnet command. Direct connection with lan cable, firewall off.

    #17819
    manjey73
    Participant

    show the log of a specific device. what data goes into it. is the device responding or just a timeout error?

    show the line and device settings.

    #17820
    manjey73
    Participant

    and actually show the device configuration in the configuration database.

    #17821
    Gabor
    Participant

    No,it looks like it does not respond at all (sending data continuously but 0 response). I started all from zero as shown in the modbus video and all worked with the simulator, however not worked on a real device. Will attach files in the afternoon as I am currently not near the setup.. Thanks in advance

    #17822
    Gabor
    Participant

    Hello, here are the photos:
    Line state:
    https://i.postimg.cc/vH2Nx8Fz/image.jpg

    Line log:
    https://i.postimg.cc/FHfnythK/image.jpg

    Device:
    https://i.postimg.cc/FK3W6jfw/image.jpg

    Device polling:
    https://i.postimg.cc/0QvW1bDP/IMG-20260412-161625-765-jpg-adding.jpg

    I am guessing it is just some silly mistake from me..

    #17823
    Gabor
    Participant

    Some more photos of the config:
    Device config:
    https://i.postimg.cc/C5xgCFhW/image.jpg

    Line Main options:
    https://i.postimg.cc/gJYFdYZr/image.jpg

    (Don’t worry about the 103…104 numbering, after getting errors, I tried with the next physical Device (103 -> 104), but did not change the project/device name, etc. Only the IP)

    #17824
    manjey73
    Participant

    Disabling the firewall does not mean that packets will be skipped.

    #17825
    Gabor
    Participant

    Yeah.. I will try next to get more info with Wireshark.

    #17826
    manjey73
    Participant

    And start with one register, specifying in the settings to start with 0 or 1. Do you also have the exact device address = 1 ? Depending on the device, the device ID may be ignored in Modbus TCP mode, or it may have to correspond to some value.

    #17827
    Gabor
    Participant

    Yes I tried with one register,and had same result. Thanks, I will try to change the device ID,maybe it is not 1. I assume I should change the Numeric Address in the device settings.. The device itself has Zero based Addresses, starting with a 32bit unsigned integer for Timestamp,the other holding registers are float type. Requesting the wrong type,address,etc. could also cause “Error:Communication failed” message?

    #17829
    manjey73
    Participant

    Yes, if the address requires 0 for the device, this may be the reason. Another option is to send a broadcast address to the device – 254 or 255 in Modbus mode when it is connected to TCP. Such things should be specified in the device documentation.

    #17832
    Gabor
    Participant

    Unfortunately I am not familiar with sending broadcast address,etc. The device documentation is very poor,or lets say simple (as per above): Zero Based Addresses for Holding registers (I received the register mapping), static IPs for the devices. But I think I have to dive deeper into this.

    #17834
    Mikhail
    Moderator

    Hi,
    According to the communication line log you can successfully connect to the device by IP, but it is not responding.
    I suppose the device ID (unit ID) is wrong as written above. Most common are 0 and 1.
    Use https://rapidscada.net/modbus/ to decode data packets. It is useful for understanding.