June 30, 2015 at 11:58 am #243
mitchok
ParticipantHi
I am trying to use Rapid SCADA to communicate with a set up Northern Design Modbus over TCP meters. It seems that communications is established but an error is being generated. Looking at the log in communicator shows ‘Incorrect PDU length’
Can someone point me in the right direction as to how I can deal with this please?
Thanks
DarrenJune 30, 2015 at 12:02 pm #244
MikhailModeratorHello Darren,
Could you write a piece of log here?June 30, 2015 at 12:14 pm #245mitchok
ParticipantSee below
Thanks
Darren2015-06-30 12:57:47 Communication session with Device 50 “CH#1”, type: KpModbus, call number: 192.168.5.19
Request element group
Send (12): 00 00 00 00 00 06 00 04 0A FF 00 01
Receive (7/7): 00 00 00 00 00 06 00
Receive (5/5): 04 0A FF 00 01
Incorrect PDU length!
Request element group
Send (12): 00 00 00 00 00 06 00 04 0A FF 00 01
Receive (7/7): 00 00 00 00 00 06 00
Receive (5/5): 04 0A FF 00 01
Incorrect PDU length!
Request element group
Send (12): 00 00 00 00 00 06 00 04 0A FF 00 01
Receive (7/7): 00 00 00 00 00 06 00
Receive (5/5): 04 0A FF 00 01
Incorrect PDU length!June 30, 2015 at 3:25 pm #246
MikhailModeratorThe device responses the same bytes as were requested.
According to MODBUS APPLICATION PROTOCOL SPECIFICATION and MODBUS MESSAGING ON TCP/IP IMPLEMENTATION GUIDE the content of the response is definitely wrong.You can get proper communication log for comparison by using Modbus emulator mod_RSsim
July 1, 2015 at 8:31 am #247mitchok
ParticipantThanks for the comments. I have tried communicating with a different unit and have had no trouble so I think I am either using the wrong address or the wrong data type
In my mind I have a vague memory that in the event of the slave not understanding the request or being unable to comply, it will repeat the request message back! Did I make this up or does this have some element of truth in it?
As you may guess, I am pretty new to this and trying to implement a metering solution on a very tight budget!
July 1, 2015 at 5:30 pm #248
MikhailModeratorProbably your vague memorials is about other protocol than Modbus )
Modbus has special error codes for such cases or device does not respond anything.
Good luck in experiments! Your questions help others to solve their issues.July 3, 2015 at 2:00 pm #249mitchok
ParticipantThanks for the help. Have managed to get that part working now. It seems I was trying to access a non-existant register !!!!!
-