ParticipantHi. I recently used Rapid for a project and I’ve been setting up a project with a Modbus device.
My only concern is that the tag values and events does not change real time. It takes 50 minutes or so for the Values to change. Do I have to purchase any driver or modules to help me with this?My Writing Period for Current Data is already set to 1second
March 25, 2022 at 7:51 am #10122
MikhailModeratorHi,
Please provide screenshots of the Communicator settings and communication line log.March 27, 2022 at 2:45 am #10125Bang
ParticipantHi,
Please refer to the link for the screenshots.
https://mega.nz/folder/IcoARZaa#_-yVQk5PtjbQ_X0-VjIMtg
Your assistance is much appreciated.
Thanks.March 27, 2022 at 2:59 am #10126Bang
ParticipantHi,
I tested it today with all the devices connected, it went well with only 5-8seconds delay on tag real time values.
I previously tested it with only one device simulated, hence the 1 minute delay on tag feedbacks.
If there’s any way to lessen the 5-8sec delay, that’d be better, if none, then that’s that.
March 28, 2022 at 7:27 am #10128
MikhailModeratorHi,
You could try the following:
1. By default, there is a delay 200 ms after each request. You can set it to 100 ms in the device options, for each device.2. Split the communication line into 2 communication lines. They work in parallel.
March 30, 2022 at 12:49 pm #10142
MerdockParticipantHello.
As a recommendation to speed up the readings I create a line for each device.
in this way, minimum times of 1 second between readings are achieved.
It is also recommended that you try to get the maximum number of records per request.
The minimum time between readings is 1 second, it is given by the writing in the Current Data file.
The Web interface takes data from this file.
This is in version 5x.
Layers that in version 6 this changed.
The Modbus Driver reads the 16 bit registers without problems.
For reading 32-bit registers, the bit order must be changed in the configuration since it does not transpose the LSBs with the MSBs and Rapid Scada reads the 2 16-bit registers consecutively.
in Default Byte Order you must put 2301.
in most cases, except device specifications. -