  • in reply to: SNMP Device Configuration – dll load error #6043
    MarCus0
    Participant

    Hi All

    Solved.
    Instaling 5.7.1 fixed problem.

    Regards

    in reply to: Send Setpoint value (float number) #4751
    MarCus0
    Participant

    Hi Again
    OK. I found something.
    It not working when I send command from communicator.
    When I created table with commands formulas started convert values as it should.

    Question, what it difference when I send command from Communicator and WebInterface?
    In Communicator I send Standard command?

    Regards

    in reply to: Send Setpoint value (float number) #4750
    MarCus0
    Participant

    Hi All

    I have similar problem and I did not find ansver there.
    I have output chanel and it working corectly when I send command directly what mean to on/off I send 256/512 value.
    To simplifiy I trying to convert to 0/1 by Formula “(Cmd*256)+256”.
    What ever I did allways I get:
    2018-12-18 20:53:32 Command to the Device 10 “Bufor_4_chanel”, type: KpModbus, address: 4
    Command “Chanel_1_cmd”
    Send (8): 04 06 00 01 00 01 19 9F
    Receive (5/5): 04 06 00 01 00
    Receive (3/3): 01 19 9F
    OK!
    what mean it sending 1 instead 512(calculated formula)?
    SCADA-Admin

    Can You help with it,please?

    in reply to: Communication errors #2457
    MarCus0
    Participant

    Hi

    Just to know.
    Bosch exchange unit(BMS Gate) and now every thing working properly.
    Thank You Mikhail for Your support.

    Regards

    in reply to: Communication errors #2273
    MarCus0
    Participant

    Hi Mikhail

    What is Your email?
    I wrote on info… but there was no answer.
    I want to ask about purchase details.

    Regards
    Marek

    • This reply was modified 6 years, 10 months ago by Mikhail.
    in reply to: Communication errors #2230
    MarCus0
    Participant

    Hi
    Modbus over serial communication working properly :).
    I will try to push on Bosch bay the way as they still not solved their problem with internal communication to external unit. We will see what they will say. Just to know.

    By the way, I’ve looked(I need to own up that thought to manipulate with KpModbus:)) at your git hub.
    Which development environment You use? It is .NET?
    I know slightly C from programming AVR’s but this is different.
    Any way code looking really nice :), really appreciate.

    Regards
    Marek

    in reply to: Communication errors #2223
    MarCus0
    Participant

    Hi

    See https://www.bosch-industrial.com/files/mng/Controllers-Accessories_Databook.pdf page 107 where is BMS-MOD described.
    There is nothing about any protocol modification and register range is similar to standard modbus. There are described web management and configuration.

    I contacted with Bosch about that but I’m not sure if I have any chance to solve this problem in that way.

    If not is there any chance to modify KpModbus.dll to omit this first length (00 06) in slave answer and just base on second byte count to calculate answer length?

    Regards
    Marek

    Regards
    Marek

    in reply to: Commands in Modbus #2219
    MarCus0
    Participant

    Hi

    “can you for example?” – You asking me or Mikhail?

    Regards

    in reply to: Communication errors #2212
    MarCus0
    Participant

    Hi

    It is looking as monologue :).

    Is possible because that:
    “Response
    01 – function code
    04 – byte count
    88 04 01 00 – Coil status”
    other software don’t care about 00 06 – following byte length?

    Regards
    Marek

    in reply to: Communication errors #2211
    MarCus0
    Participant

    Hi
    Finding continued.
    In spec http://www.modbus.org/docs/Modbus_Application_Protocol_V1_1b3.pdf page 11 about functions
    You can find PDU from last readings:
    Request
    01 – fuction code
    02 80 – starting adress
    00 20 – quantity of coils(32dec)
    Response
    01 – function code
    04 – byte count
    88 04 01 00 – Coil status

    And MBAP Header:
    00 02(01) – transaction identifier. In communicator it seems not implemented and can make some problem as TCP is not direct query/answer. Datagrams can be send in different order(http://modbus.org/docs/Modbus_Messaging_Implementation_Guide_V1_0b.pdf page 16).
    00 00 – protocol identifier. Always 00 00 for modbus.
    00 06 – it should be PDU+UnitIdendifier byte but ?! it is not in gate answer. I will look for explanation but this field in all examples are 00 06 and unfortunately all examples match this number. I don’t know why Gate not calculate message length and why it is OK. for other software’s?
    02 – Unit identifier(address)

    It seems that only problem is in lenght PDU+UI byte. When I change response manually(lenght) answer is OK in Your parser and will be probably OK. in Communicator.

    Is any other chance to solve it than contact Bosch? Can we omit this length control as other software do?

    Regards
    Marek
    Re

    in reply to: Communication errors #2209
    MarCus0
    Participant

    Hi

    See this from Communicator when I set 32 coils to read.
    https://ibb.co/e7MJiF
    There are messages about Incorrect MBAP Header data.

    There is correct answer from SimplyModbus https://ibb.co/fgr13F

    Regards
    Marek

    • This reply was modified 6 years, 10 months ago by MarCus0.
    in reply to: Communication errors #2208
    MarCus0
    Participant

    Hi

    It is nothing change. What ever I try is error about communication error but Mikhail answers in comunicator are the same then other softaware?
    Just Communicator expect additional bytes which are not send by Gate than we get immediately is error.
    It is funny but on http://www.simplymodbus.ca/TCP.htm page is protocol explanation and their software not follow them. 06 mean that we should expect 6 bytes. In answers are 4 and every other software(Simlymodbus and Modpoll) accept it properly.

    I’m tried manually on (http://modbus.rapidscada.net/) modify Gate answers but without luck. Later I will try to look for where is truth with protocol and possible problem explanation.

    Perhaps You know how to solve it? I cant modify any Gate settings(there is nothing to set about communication as is closed solution) as is comply with popular software I cant claim it.
    Is a first time with You get such error? Is any body implement TCP(instead Modbus over TCP) protocol on Communicator? My problem is first?

    Regards
    Marek

    in reply to: Commands in Modbus #2200
    MarCus0
    Participant

    Hi
    Check please Your template where You define addresses conversion from Modbus table to Communicator Chanel’s.
    Regards
    Marek

    in reply to: Communication errors #2196
    MarCus0
    Participant

    Hi
    See this one
    https://ibb.co/bZUbLv
    Regards
    Marek

    in reply to: Communication errors #2185
    MarCus0
    Participant

    Hi again

    I tried Simply Modbus http://www.simplymodbus.ca/SimplyModbusTCPclient7.1.2Install.zip
    Results You can see here http://i66.tinypic.com/jac09w.png. It seems that Gate answer properly.
    I tried always read the same 10 coils from 00641 address.
    For request: 00 00 00 00 00 06 02 01 02 80 00 0A, answer: 00 01 00 00 00 06 02 01 02 88 02 is proper in ModbusPoll and in Simly Modbus software but Communicator and online http://modbus.rapidscada.net/ is generating error.

    Can You check where is problem, please?

    Regards
    Marek