MikhailModerator
Formula of the input channel would be:
Stat() > 0 ? 1 : 0Also you need to select Format = Enum text and Unit = Off-On
MikhailModeratorMikhailModeratorif ScadaWebCommon5.dll exists, delete it. The actual library is ScadaWebCommon.dll
Also make sure that Chart Pro plugin is up to date.The repository provides more info about version compatibility.
MikhailModeratorSimilar situation can occur if you change ScadaAdmin password. In this case, export the User table to user.dat and copy to the server manually.
MikhailModeratorThe above link is not available for me.
MikhailModeratorUse the Stat function in your formulas.
MikhailModeratorThat’s right.
MikhailModeratorPlease clarify your question.
February 25, 2020 at 4:06 pm in reply to: simple Formula that compares an Integer or real and returns Boolean #6558MikhailModeratorIn Rapid SCADA all input channel values have the double type. Double is a 64-bit floating point.
February 25, 2020 at 5:55 am in reply to: simple Formula that compares an Integer or real and returns Boolean #6552MikhailModeratorHi,
Try this:
Val(60) == 33 ? 1 : 0; Stat(60)
However, it’s a bag practice to compare floating point values by equality operator. It’s better to use <= or >=
MikhailModeratorYou should provide screenshots of the Interface table and of the deployment profile.
MikhailModeratorHello,
Please check what user name and password are specified in the deployment profile options.MikhailModeratorHi,
Also noticed that /opt/scada/ScadaWeb had infinite directories
Haven’t faced this before.
MikhailModeratorHi,
There should be 2 connections to SCADA-Server, by the users ScadaComm and ScadaWeb.
Please check what is written in ScadaServerSvc.txt about active connections.
Also check ScadaCommSvc.log and ScadaWeb.logMikhailModeratorIn Administrator create a new deployment profile for Raspberry. Upload all the configuration except Server settings (because they have different file paths).
-