MikhailModerator
May be we should change the size from 10485760 to 104857600 by default.
MikhailModeratorIt means that the configuration is too big (more than 10 MB). When configuration is transferred, it is zipped to reduce size. So 10 MB is a size of an archive.
There are 2 options how to fix:
1. Check your interface files. May be you should optimize images.
2. Increase maxReceivedMessageSize in C:\SCADA\ScadaAdmin\ScadaAdmin.exe.config- This reply was modified 3 years, 8 months ago by Mikhail.
MikhailModeratorHi,
1. Read the registers from 30215 to 30218 as a double (8 bytes) in Communicator. They will be passed to a one input channel.
2. Check the displayed value.Share new screenshots, please.
MikhailModeratorHello Irene,
It looks like the configuration file of Chart Pro is not included in the project. Please find PlgChartPro.xml in the distributive package of Chart Pro and copy it to YourProject\Instances\Default\ScadaWeb\config\ directory.
Then upload the project to the server.MikhailModeratorHi,
Chart Pro supports export channel values to Excel.
MikhailModeratorHello,
The additional error information is in C:\SCADA\ScadaAdmin\Log\ScadaAdmin.err
Please provide the error details from the log.MikhailModeratorMin and Max are constants. That’s true. As a work around you could create an extra input channel of the Calculated type. And set a formula to calculate some kind of relational value.
i would like the right picture, but the colors of the ring changing with time regarding a variable bandwidth.
The right picture uses a background found somewhere in the internet. A display over a gauge is a dynamic text component.
MikhailModeratorThe values in the table, also black, not red and green. This means that input channels are not configured properly. You should also set the Unit field to Off-On.
MikhailModeratorPlease contact us by email for more info.
MikhailModeratorCreate a table view to check color of values.
MikhailModeratorSorry, I mean:
Open Line 2 Parameters – Request Sequence, select the device 1 and then make a screenshot.MikhailModeratorHello,
It’s possible to deploy a virtual machine in the cloud (Google, Azure, AWS, etc.) and install Rapid SCADA on that machine.
For our servers we use different providers. You should select your favorite.
MikhailModeratorDid you upload the project after change?
Create a table view to check color of values.MikhailModeratorHi,
You need Automatic Control Module for this purpose.
MikhailModeratorChange channel type to Discrete
-