by any chance is it possible to use a V5 SCADA with Rapid Gate to connect to a V6 ?
if I upgrade from V5 (delete all) and install new V6 (latest, windows), the computer code and the license remains the same?
on V6 is it possible to change the layout of the landing page (main page) as it was on V5?
masl999ParticipantHi, the convert V5 to V6 worked with some issues, one that i am having problem is that the unit of the converted v6 has changed:
V5= <UnitID>67</UnitID>
V6= <UnitID>1</UnitID>Any hint to fix it or to scan manually each variable?
<InCnl>
<CnlNum>4297</CnlNum>
<Active>true</Active>
<Name>TP_CxPermeado_2017</Name>
<CnlTypeID>3</CnlTypeID>
<ObjNum>3</ObjNum>
<KPNum>51</KPNum>
<Signal xsi:nil=”true” />
<FormulaUsed>true</FormulaUsed>
<Formula>(((Val(4288)/100)+0.15))>5 ? 5:(((Val(4288)/100)+0.15))</Formula>
<Averaging>false</Averaging>
<ParamID xsi:nil=”true” />
<FormatID>2</FormatID>
<UnitID>67</UnitID>
<CtrlCnlNum xsi:nil=”true” />
<EvEnabled>false</EvEnabled>
<EvSound>false</EvSound>
<EvOnChange>false</EvOnChange>
<EvOnUndef>false</EvOnUndef>
<LimLowCrash xsi:nil=”true” />
<LimLow xsi:nil=”true” />
<LimHigh xsi:nil=”true” />
<LimHighCrash xsi:nil=”true” />
</InCnl><Cnl>
<CnlNum>4297</CnlNum>
<Active>true</Active>
<Name>TP_CxPermeado_2017</Name>
<DataTypeID xsi:nil=”true” />
<DataLen xsi:nil=”true” />
<CnlTypeID>3</CnlTypeID>
<ObjNum>3</ObjNum>
<DeviceNum>51</DeviceNum>
<TagNum xsi:nil=”true” />
<TagCode />
<FormulaEnabled>true</FormulaEnabled>
<InFormula>(((Val(4288)/100)+0.15))>5 ? 5:(((Val(4288)/100)+0.15))</InFormula>
<OutFormula />
<FormatID>4</FormatID>
<OutFormatID xsi:nil=”true” />
<QuantityID xsi:nil=”true” />
<UnitID>1</UnitID>
<LimID xsi:nil=”true” />
<ArchiveMask xsi:nil=”true” />
<EventMask xsi:nil=”true” />
</Cnl>masl999ParticipantI belive i found the error; formula dividing by Zero when asked to display at the screen
masl999ParticipantI have a similar error, trying to open a page show the error “Error updating scheme data”.
The RapidScada was working fine for about a year without a issue and started this. Already tried to delete DAT files and a few other things and did not work.
Specifications:
Windows 2008 Server
.Net Framework 4.8
Administrator 5.5.2.1
Communicator 5.2.1.0
Server 5.1.4.0https://ibb.co/8YfGHY2