robybobParticipant
Hi Mikhail,
sure, you are perfectly right concerning that increasing size of queue will not solve the problem, but it might help in delaying it. It would be just a temporary workaround as I am afraid that after a few days, process stucks and stops sending data (as it was before changing delays).
BTW my email is: … and I will be waiting for your email.Regards
Robybob- This reply was modified 4 years, 10 months ago by Mikhail.
robybobParticipantWell Mikhail, thank you for offering a remote connection, but I would need an official offer for support and costs in the case.
In the time between I might give a more clear idea what there is behind this issue:
– scadaComm has 7 Modbus channels. Each channel has about 60 elements to interrogate and gather values. Elements are grouped into 12 element group and delay between each group interrogation is 2 secs. Finally delay per each sequence is 30 sec.Well, according log, ScadaComm starts regularly without any alarm, after about 4 hours a first queue overflow alarm is coming out. Then the alarm frequency increases.
`2019-06-14 08:20:57 Start ModDBExport module
2019-06-14 08:24:05 Module ModDBExport is stopped
——————————————————————————–
——————————————————————————–
2019-06-14 08:24:07 Start ModDBExport module
2019-06-14 11:04:07 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:04:07 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:07:32 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:08:50 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:15:20 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:16:39 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:17:57 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:19:15 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:20:33 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:22:58 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:24:16 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:25:34 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:26:52 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:29:39 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:30:47 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:33:23 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:33:33 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:34:51 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:35:59 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:36:07 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:36:07 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:38:23 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:38:45 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 11:41:38 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
`So I might deduct (maybe wrongly) that problem could be in performance and/or is queue too short for my implementation.
BTW you should have my email where to write your offer for remote support/assistance.
Thank you so much
RobybobrobybobParticipantHere you are,
well I have increased the delay to 2000 ms but I am getting a queue overflow:`2019-06-14 05:41:59 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 05:46:28 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 05:48:52 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 06:20:54 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 06:22:30 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 06:38:36 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 06:39:02 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 07:18:05 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 07:25:46 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
2019-06-14 07:32:59 Unable to enqueue an event. The maximum size of the queue 100 is exceeded
”
Do you think I am getting a performance issue of rapidscada ?Regards
RobybobrobybobParticipantHi Mikhail,
correct, I have switched off events in order to find out who is causing the error in error log. I don’t have any clue where clause ‘Infinity’ is coming out and I would add a similar error coming out with ‘NaN’ instead of ‘Infinity’.
I doubt there are other configurations running but I will check out in the case I left some residuals from a previous installation.
I may add some more information:
– mysql dB is running in the same HW where rapidscada is located, when upgrading to 5.6.1 from 5.6.0 (where no errors where present) I rebuild completely ServerComm configuration (modbus) in order to respect your document and indications.
– mysql log doesn’t state any import error (maybe I need to activate verbosity to get it).
Latest: another error is coming out
Unable to enqueue an event. The maximum size of the queue 100 is exceeded
Is there a way to enlarge output queue ?robybobParticipantHi Mikhail,
I am sorry to bother you again.
Well, server where the error is present is Ubuntu, so I can post you the XML
of the Server:<?xml version="1.0" encoding="utf-8"?> <ModDBExport> <ExportDestinations> <ExportDestination> <DataSource> <DBType>MySQL</DBType> <Server>192.168.20.50</Server> <Database>rapid</Database> <User>ScadaServerCtrl</User> <Password>rapidscada</Password> <ConnectionString /> </DataSource> <ExportParams> <ExportCurData>true</ExportCurData> <ExportCurDataQuery>INSERT INTO cnldata (datetime, cnlnum, val, stat) VALUES (@dateTime, @cnlNum, @val, @stat)</ExportCurDataQuery> <ExportArcData>true</ExportArcData> <ExportArcDataQuery>INSERT INTO cnldata (datetime, cnlnum, val, stat) VALUES (@dateTime, @cnlNum, @val, @stat) ON DUPLICATE KEY UPDATE val = @val, stat = @stat</ExportArcDataQuery> <ExportEvents>false</ExportEvents> <ExportEventQuery>INSERT INTO events (datetime, objnum, kpnum, paramid, cnlnum, oldcnlval, oldcnlstat, newcnlval, newcnlstat, checked, userid, descr, data) VALUES (@dateTime, @objNum, @kpNum, @paramID, @cnlNum, @oldCnlVal, @oldCnlStat, @newCnlVal, @newCnlStat, @checked, @userID, @descr, @data)</ExportEventQuery> </ExportParams> </ExportDestination> </ExportDestinations> <ManualExport> <CurDataCtrlCnlNum>1</CurDataCtrlCnlNum> <ArcDataCtrlCnlNum>2</ArcDataCtrlCnlNum> <EventsCtrlCnlNum>3</EventsCtrlCnlNum> </ManualExport> </ModDBExport>
If this is not sufficient, I might find out the original rapid scada server configuration and forward Config screenshots.
Let me know
RobybobrobybobParticipantHi Mikhail,
it is working !!!copying ‘MySql.Data.dll to SCADA/ScadaServer/‘ solved the problem.
Sorry I didn’t realized before posting stupid things.Thank you
Robybob -