  • in reply to: OPC write value issue-IBH opc server #4516
    mariodavid
    Participant
    in reply to: OPC write value issue-IBH opc server #4490
    mariodavid
    Participant

    https://imgur.com/a/5z1tsaN

    https://imgur.com/a/lW7E584

    I found this in the library OpcComRcw. How do I implement this in the KpOpclogic?

    in reply to: OPC write value issue-IBH opc server #4489
    mariodavid
    Participant

    Hi, I am using mpi/usb protocol to connect to plc s7-300. I have not found another server that is compatible with mpi / usb. There is SIMATIC NET but is paid.

    in reply to: OPC write value issue-IBH opc server #4478
    mariodavid
    Participant

    http://www.diit.unict.it/users/scava/dispense/II_270/OPCDACOMOverview.pdf

    said that IOPCSyncIO is required in Data Access Server 1,2 and 3.

    in reply to: OPC write value issue-IBH opc server #4477
    mariodavid
    Participant

    “In the source code I just use daServer.Write(new Opc.Da.ItemValue[] { itemVal }); and the library made by OPC Foundation choose lo-level method WriteVQT”.

    the library made by OPC Foundation are not free but, Is there another method using the same library?

    I am sure that I can write with this method: IOPCSyncIO::Write

    in reply to: OPC write value issue-IBH opc server #4476
    mariodavid
    Participant

    OPC_E_NOTSUPPORTED 0xC0040406 If a client attempts to write any value, quality,
    timestamp combination and the server does not
    support the requested combination (which could
    be a single quantity such as just timestamp), then
    the server will not perform any write and will
    return this error code.

    I found it here: https://digitalsupport.ge.com/servlet/fileField?id=0BE1A000000TPEf

    the opc libraries are paid,
    Is there any other way to use other libraries to use another method?

    in reply to: OPC write value issue-IBH opc server #4475
    mariodavid
    Participant

    Hi, I replaced the new file with the previous one in the folder SCADA/ScadaComm/KP.

    opc analyzer:

    OPC Analyzer Trace – Application Version 1.2.1012
    saved on mar 23. oct 12:43:06 2018

    12:42:40.810 – IOPCItemIO::WriteVQT ————————————————————-
    General:
    HRESULT: 0x00000001 S_FALSE

    In Parameters:
    pszItemIDs:
    [0] = PLC1.Generic.ACTIVAR_VALVULA_T1
    dwCount: 1
    pItemVQT:
    Item 0:
    vDataValue = VT_BOOL -1
    bQualitySpecified = TRUE
    wQuality = 0x00c0 OPC_QUALITY_GOOD
    bTimeStampSpecified = FALSE
    ftTimeStamp = 1601-01-01T00:00:00.000

    Out Parameters:
    ppErrors:
    [000] 0xc0040406 OPC_E_NOTSUPPORTED

    in reply to: OPC write value issue-IBH opc server #4455
    mariodavid
    Participant
    in reply to: OPC write value issue-IBH opc server #4453
    mariodavid
    Participant

    Hi.

    please let me know, I really need to write that tags.

    in reply to: OPC write value issue-IBH opc server #4446
    mariodavid
    Participant

    Hello.

    I try with 2.XX and and the same thing happens. Marc:

    “Hello Mario,

    I have been able to install rapid scada and am currently testing this on our system. I am having some trouble issuing a write – how are you doing that exactly on your end?

    The reason I do not think this is an issue with the IBH server is that it actually responds with a “success” so I would expect that the write has been processed correctly – this is something I would like to see here on my end.

    Kind Regards,

    Marc”

    Is it possible to write with IOPCSyncIO::Write?

    in reply to: OPC write value issue-IBH opc server #4443
    mariodavid
    Participant

    Hi. The developer does not answer yet. I have been searching and some servers are not compatible with writeVQT method. https://advosol.com/manuals/opcdanet/topic177.html

    Is there the possibility of writing with another method?

    in reply to: OPC write value issue-IBH opc server #4406
    mariodavid
    Participant

    Will there be any difference if I use the 5.5.3 version? I am using 5.5.2 rapid scada version.

    in reply to: OPC write value issue-IBH opc server #4405
    mariodavid
    Participant

    developer wrote: Hello Mario,

    “The issue here is that the WriteVQT is writing a value of -1 (high) and a quality of Bad. Where the Quick Client write is only writing a -1 (high). Your other client needs to not write the quality bad if you want the quality to remain good and the write succeed.

    Why is the rapid scada writing a bad quality? OPC Specs declare that the value is undefined if OPC quality is bad, so the server is not processing the write.

    Thanks,
    Marc”

    in reply to: OPC write value issue-IBH opc server #4404
    mariodavid
    Participant

    developer wrote: Hello Mario,

    “The issue here is that the WriteVQT is writing a value of -1 (high) and a quality of Bad. Where the Quick Client write is only writing a -1 (high). Your other client needs to not write the quality bad if you want the quality to remain good and the write succeed.

    Why is the rapid scada writing a bad quality? OPC Specs declare that the value is undefined if OPC quality is bad, so the server is not processing the write.

    Thanks,
    Marc”

    in reply to: OPC write value issue-IBH opc server #4373
    mariodavid
    Participant

    I use opc analyzer with quick ckient and rapid scada. this is the log.

    first, quick client:

    “OPC Analyzer Trace – Application Version 1.2.1012
    saved on mar 9. oct 12:09:15 2018

    12:08:35.437 – IOPCSyncIO::Write —————————————————————-
    General:
    GroupName: PLC1.Generic
    GroupServerHandle: 0x5721688
    HRESULT: 0x00000000 S_OK

    In Parameters:
    pItemValues:
    [000] VT_BOOL -1
    dwCount: 1
    phServer:
    [000] 0x06895348

    Out Parameters:
    ppErrors:
    [000] 0x00000000 S_OK

    12:08:35.967 – IOPCDataCallback::OnDataChange —————————————————
    General:
    HRESULT: 0x00000000 S_OK
    GroupName: GRP06897320
    numCallbacks: 10
    minTime: 54.974 ms
    averageTime: 134.769 ms
    GroupServerHandle: 0x302398
    maxTime: 508.228 ms
    CallTime: 101.790 ms

    In Parameters:
    hrMasterquality: 0x00000000 S_OK
    pvValues:
    [000] VT_BOOL -1
    [001] VT_BOOL -1
    [002] VT_BOOL -1
    dwCount: 3
    hrMastererror: 0x00000000 S_OK
    pftTimeStamps:
    [000] 2018-10-09T16:08:35.608
    [001] 2018-10-09T16:08:35.718
    [002] 2018-10-09T16:08:35.718
    dwTransid: 0
    phClientItems:
    [000] 0x00000008 [001] 0x0000000b [002] 0x00000013
    hGroup: 0x0
    pwQualities:
    [000] 0x00c0 OPC_QUALITY_GOOD
    ::::
    [002] 0x00c0 OPC_QUALITY_GOOD
    pErrors:
    [000] 0x00000000 S_OK
    ::::
    [002] 0x00000000 S_OK

    12:08:36.014 – IOPCDataCallback::OnDataChange —————————————————
    General:
    HRESULT: 0x00000000 S_OK
    GroupName: PLC1.Generic
    numCallbacks: 11
    minTime: 0.139 ms
    averageTime: 0.429 ms
    GroupServerHandle: 0x5721688
    maxTime: 2.238 ms
    CallTime: 0.192 ms

    In Parameters:
    hrMasterquality: 0x00000000 S_OK
    pvValues:
    [000] VT_BOOL -1
    [001] VT_BOOL -1
    [002] VT_BOOL -1
    dwCount: 3
    hrMastererror: 0x00000000 S_OK
    pftTimeStamps:
    [000] 2018-10-09T16:08:35.718
    [001] 2018-10-09T16:08:35.608
    [002] 2018-10-09T16:08:35.718
    dwTransid: 0
    phClientItems:
    [000] 0x003d4608 [001] 0x003d42f8 [002] 0x003d4138
    hGroup: 0x3e2fe8
    pwQualities:
    [000] 0x00c0 OPC_QUALITY_GOOD
    ::::
    [002] 0x00c0 OPC_QUALITY_GOOD
    pErrors:
    [000] 0x00000000 S_OK
    ::::
    [002] 0x00000000 S_OK

    12:08:39.009 – IOPCDataCallback::OnDataChange —————————————————
    General:
    HRESULT: 0x00000000 S_OK
    GroupName: GRP06897320
    numCallbacks: 11
    minTime: 54.974 ms
    averageTime: 132.910 ms
    GroupServerHandle: 0x302398
    maxTime: 508.228 ms
    CallTime: 114.316 ms

    In Parameters:
    hrMasterquality: 0x00000000 S_OK
    pvValues:
    [000] VT_BOOL -1
    [001] VT_BOOL 0
    dwCount: 2
    hrMastererror: 0x00000000 S_OK
    pftTimeStamps:
    [000] 2018-10-09T16:08:38.588
    [001] 2018-10-09T16:08:38.588
    dwTransid: 0
    phClientItems:
    [000] 0x00000004 [001] 0x00000008
    hGroup: 0x0
    pwQualities:
    [000] 0x00c0 OPC_QUALITY_GOOD
    [001] 0x00c0 OPC_QUALITY_GOOD
    pErrors:
    [000] 0x00000000 S_OK
    [001] 0x00000000 S_OK

    12:08:39.040 – IOPCDataCallback::OnDataChange —————————————————
    General:
    HRESULT: 0x00000000 S_OK
    GroupName: PLC1.Generic
    numCallbacks: 12
    minTime: 0.139 ms
    averageTime: 0.407 ms
    GroupServerHandle: 0x5721688
    maxTime: 2.238 ms
    CallTime: 0.159 ms

    In Parameters:
    hrMasterquality: 0x00000000 S_OK
    pvValues:
    [000] VT_BOOL -1
    [001] VT_BOOL 0
    dwCount: 2
    hrMastererror: 0x00000000 S_OK
    pftTimeStamps:
    [000] 2018-10-09T16:08:38.588
    [001] 2018-10-09T16:08:38.588
    dwTransid: 0
    phClientItems:
    [000] 0x003d44b8 [001] 0x003d42f8
    hGroup: 0x3e2fe8
    pwQualities:
    [000] 0x00c0 OPC_QUALITY_GOOD
    [001] 0x00c0 OPC_QUALITY_GOOD
    pErrors:
    [000] 0x00000000 S_OK
    [001] 0x00000000 S_OK”

    rapid scada:

    “OPC Analyzer Trace – Application Version 1.2.1012
    saved on mar 9. oct 12:11:09 2018

    12:10:15.964 – IOPCItemIO::WriteVQT ————————————————————-
    General:
    HRESULT: 0x00000000 S_OK

    In Parameters:
    pszItemIDs:
    [0] = PLC1.Generic.bandera_ESB
    dwCount: 1
    pItemVQT:
    Item 0:
    vDataValue = VT_BOOL -1
    bQualitySpecified = FALSE
    wQuality = 0x0000 OPC_QUALITY_BAD
    bTimeStampSpecified = FALSE
    ftTimeStamp = 1601-01-01T00:00:00.000

    Out Parameters:
    ppErrors:
    [000] 0x00000000 S_OK”