Viewing 15 posts - 136 through 150 (of 923 total)
  • in reply to: Using Internal variables/channels #16650
    SetVal(500.34) does not work, presumably because the Val() formula cannot display the channel value without a status. I also came across this. There is also the Data() formula, but I haven’t tried it yet, somehow it wasn’t necessary. It works a little differently, if I understood correctly.
    You can change the values from the range directly in the channel formula, try using the combined CheckComm formulas inside the SetVal formula as shown above.
    If you plan to use formulas inside other formulas, make it a rule to convert to double yourself, even if returning bool is enough for you. Then it becomes possible.
    in reply to: Using Internal variables/channels #16649
    CheckComm – The multiplier formula
    CheckComm1 – The formula is without using a multiplier, in fact, the multiplier is 1 if you use the first one
    in reply to: Using Internal variables/channels #16648
    public double CheckComm(double min, double max, double mult, string str = "" )
    if (Cmd < min || Cmd > max) throw new Exception($"The value must be within {min} - {max} {str}");
    return Cmd*mult;
    public double CheckComm1(double min, double max, string str = "" )
    return Cmd;
    You can also use formulas with verification to control the input parameters.
    I’ve been making universal ones for myself here.
    The method of application in the output formula of the channel
    Output channel
    CheckComm(16, 32, 10, "degrees")
    Calculated/Output
    SetVal(CnlNum, CheckComm(16, 32, 10, "degrees"))
    in reply to: Using Internal variables/channels #16647
    Try different options, as different channel processing scripts are required for different tasks.
    in reply to: Using Internal variables/channels #16646
    Input and Outputs Scrips
    An example of using formulas in Calculated channels
    The Val() formula allows you to show the value after you enter it, but it will reset on reboots.
    There is a formula that allows you to use the default value for reboots, suggested by Mikhail.
    // Set the default setpoint value.
    // For channels of the Calculated/output type
    public CnlData GetDefaultData(double val)
      return Stat() > 0 ? Data() : NewData(val, 1);
    in reply to: Using Internal variables/channels #16644
    you need to use formulas in channels. the simplest is Val() for input and SetVal(CnlNum, Cmd) for output formulas.
    well, there is also the possibility of using more complex formulas. The channel must be Calculated/Output
    in reply to: Faster thread #16642
    Start with scripts in which you read or write to files, and the like. That is, some more complex scripts that you use.
    in reply to: Faster thread #16635
    You’ve voiced the problem, but you haven’t provided a single script that you think could lead to this.
    in reply to: Faster thread #16633
    so 10 times per second is about a 100ms cycle 🙂
    in reply to: Faster thread #16629
    Please show me your script.
    When calling the script directly, it should run faster than when called through EverySec.
    in reply to: Faster thread #16627
    I don’t understand how your script works fast when using the limit of once per second (everysecond) and at the same time runs for 10 seconds with a direct call?
    Show your script that behaves this way.
    in reply to: Faster thread #16624
    1. How does your script run for a few seconds without using EverySec?
    How did you determine that?
    in reply to: Faster thread #16622
    You can use it inside your scripts. Someone also has to set the timer so that it starts working.
    in reply to: Faster thread #16621
    What’s wrong with processing a script in a loop, which also requires a timer of less than a second?
    To be honest, I haven’t implemented timers for such a task. I usually use them for other purposes, for example, to delay triggering the device status.
    What exactly is your goal? Can you draw a flowchart for understanding?
    An example of a TON timer from CodeSys or similar.
    // IEC timers and others
    public static long Ticks()
    DateTime now = DateTime.Now;
    long time = now.Ticks/10000;
    return time;
    protected class UtilTimer
    public long et;
    public bool flag;
    public bool q;
    protected Dictionary<string, UtilTimer> TonTimer = new Dictionary<string, UtilTimer>();
    protected Dictionary<int, UtilTimer> TofTimer = new Dictionary<int, UtilTimer>();
    protected Dictionary<int, UtilTimer> TpTimer = new Dictionary<int, UtilTimer>();
    // Timer with a delay of turning on TON
    public double TON(double IN, double PT, double Q, string str = "", int idx = 0)
    var ut = new UtilTimer() {et = 0L, flag = false, q = false};
    string keys = $"{CnlNum}_{idx}"; // The key is the channel number plus the timer index, zero by default. Allows you to use multiple timers inside a formula.
    long ET  = 0L;
    long _pt = Convert.ToInt64(PT);
    bool q   = Q > 0;
    bool _in = IN > 0;
    string s = str.ToLower();
    if (s == "s" || s == "sec") _pt = Convert.ToInt64(PT) * 1000;
    if (s == "m" || s == "min") _pt = Convert.ToInt64(PT) * 60000;
    if (s == "h" || s == "hour") _pt = Convert.ToInt64(PT) * 3600000;
    if (!TonTimer.ContainsKey(keys))
        TonTimer.Add(keys, ut);
    if (!_in)
        TonTimer[keys].q = false;
        TonTimer[keys].flag = false;
        TonTimer[keys].et = 0L;
    else
        if (!TonTimer[keys].flag)
        TonTimer[keys].flag = true;
        TonTimer[keys].et = Ticks();
     else
         if (!q) ET = Ticks() - TonTimer[keys].et;
     if (ET >= _pt) q = true;
     TonTimer[keys].q = q;
    q = TonTimer[keys].q;
    return Convert.ToDouble(q);
    // Timer with delayed shutdown of TOF
    public double TOF(double IN, double PT)
    var ut = new UtilTimer() {et = 0L, flag = false};
    long ET = 0L;
    bool q = Val(CnlNum) > 0;
    bool _in = IN > 0;
    if (!TofTimer.ContainsKey(CnlNum))
    TofTimer.Add(CnlNum, ut);
    if (_in)
    q = true;
    TofTimer[CnlNum].flag = true;
    TofTimer[CnlNum].et = 0L;
    ET = 0L;
    else
    if (TofTimer[CnlNum].flag)
    TofTimer[CnlNum].flag = false;
    TofTimer[CnlNum].et = Ticks();
    ET = 0L;
     else
       if (q) ET = Ticks() - TofTimer[CnlNum].et;
     if (ET >= _pt) q = false;
    // Pulse Timer TP
    public double TP(double IN, double PT)
    long ET = 0L;
    bool _in = IN > 0;
    if (!TpTimer.ContainsKey(CnlNum))
    TpTimer.Add(CnlNum, ut);
    if (!TpTimer[CnlNum].flag)
     if (_in)
     TpTimer[CnlNum].flag = true;
     TpTimer[CnlNum].et = Ticks();
     if (ET < _pt) q = true;
    else
      if (q)
      ET = Ticks() - TpTimer[CnlNum].et;
      else
       if(!_in)
       TpTimer[CnlNum].flag = false;
       ET = 0L;
    in reply to: Faster thread #16619
    All formulas in the channels are executed in a cycle from the smaller channel to the larger one. If you don’t specify every second, then it’s about 10 times per second. And the more channels there are, the longer the pause time will be.
    Or don’t use the every second wrapper, or use your own timer for example.