  • in reply to: Modbus WAGO #2681
    peter_f
    Participant

    The problem seems to besolved solved.
    The range 12288 to 24575 is Modbus-address. I don’t kow why, but apparently rapid scada divides 1, so that scada address 1 appears as standart Modbus-address 0. I set the offset to 12288 so I requested data from standart address 12287. This is a reseved range with no valid data. This seems to be the reason for the occured error.

    in reply to: Modbus WAGO #2678
    peter_f
    Participant

    Hi Mikhail,

    in the manual of the WAGO-Controller stands that the Modbus-Addressrange is from 12288 to 24575. If I use Modbuspoll to read the values without giving an offset, I get the same strange result as in rapid scada. In Modbus poll there is a window called Read/write Definition where i can define an address (It seems to be somethin like a startaddress). If I define 12288 as address I can read the Addresses above 12288 with the correct value. The equivalent setting in rapid scada seems to be in the template. There is a field start element address. If I write at this point 12288, it causes errors.
    So I would say that the values are not at that position scada expects. I think this is a problem of WAGO but I hope scada can handle it.
    Is this what you need to know?

    in reply to: Modbus WAGO #2675
    peter_f
    Participant

    What I forgot to say ist, that I tried to solve this problem by inserting 12288 in the Address-column of Device table. This was not successful.