Viewing 15 posts - 841 through 855 (of 981 total)
  • in reply to: Show time on the scheme #5752
    Yes, we need a formula.
    Make a calculation channel, specify the use of the formula. As a formula, specify
    DateTime.Now.ToOADate()
    Set the display format to Time, Date or Date and Time
    Display the channel in a table or scheme
    in reply to: How can I do #5737
    Using Modbus in Siemens PLC
    in reply to: Version number change #5666
    Thanks, look. I’m really gonna have to deal with the DF1, the Micrologix controller.
    in reply to: Formulas check '-' #5662
    Look for formulas to check the signal status on the forum or try to change the formula to double.NaN
    in reply to: Unknown device tags #5656
    Does your PLC work via Ethernet or com port ? Can you make a log of Wireshark or monitoring program for COM port and put on the file exchanger ?
    With the exact model of PLC ? and the type of exchange Protocol ?
    • This reply was modified 7 years, 3 months ago by manjey73.
    in reply to: Communication with Multiple Devices #5618
    We need to spread the devices on different physical lines of communication.
    in reply to: Unknown device tags #5616
    Could you share the wireshark logs that you received by scanning the packets ? If anything, there is the Allen Bradley Protocol.
    in reply to: Unknown device tags #5598
    You can check if this applies to Modbus using this link
    Rapid SCADA Modbus Parser
    However, you need to find the right start and end of the parcel in the TCP scanner
    in reply to: Unknown device tags #5593
    There is a similar task, but AB Micrologix is used, according to the description PLC data support Modbus, but it is used or not unknown. You must put the port watcher on the exchange between the PLC and the HMI panel to read the traffic between them. But not the fact that it will help. Plus, try to connect to the PLC with Modbus scanners.
    Google Переводчик
    in reply to: Could you help to make correct logic. #5452
    Tell me, why do you then need to input 1 ?
    in reply to: Automatic control with Raspberry Pi #5257
    It is also necessary to transfer the configuration of the module settings. And also buy a license for the module on RaspberryPi
    in reply to: Rapid Gate #5167
    If the server is one of the main, the Rapid Gate is not needed.
    If there are several servers plus one main server, then Rapid Gate is needed for each slave server and the corresponding number of licenses for each Rapid Gate is required.
    A large diagram is specified without Rapid Gate
    • This reply was modified 7 years, 7 months ago by manjey73.
    in reply to: Address Modbus RTU #5140
    Command type – Binary ??????? may ba Standard
    And you need to pass 0 or 1 ?
    in reply to: TCP/IP or MQTT #5119
    On the site your GSM modem can establish a connection via VPN channel ?
    in reply to: Save #5073
    See Dat files in folders c:\SCADA\ArchiveDAT\
    The data can be viewed using the Server application