    Hi collegues,
    I’m new to rapidscada, after a short training I could connect a device (a power meter) to the software with a direct ethernet connection with the pc.
    Now I assigned a static ip address to my device, so I can access to its internal webserver through the web.
    I went then to rapidscada and I changed its local ip address into the public ip address, i kept the port 502, it did not connect. can anyone tell me what’s wrong ?
    Thanks

    #2636
    Mikhail
    Mikhail
    Moderator

    Hi,
    Please paste communication line log here.
    You should check firewall. Probably, outgoing connection to TCP port 502 is prohibited. Web interface uses port 80 which is usually permitted.

    #2641

    Riadh
    Participant

    Hi Mikhail, I have set the port on 443 and it worked, thanks.